Only if you ignore the statement in GN3 that cpc continuity can be verified through live loop testing. Dead testing for cpc continuity is designed to ensure that the installation is not energised with unearthed parts. This caution is no longer necessary when the installation is already energised, as any potential danger already exists.I would therefore draw from the IET statement that a complete suite of tests (dead and live) should be done in a domestic situation unless there is good cause not to do so )or for some reason it has been agreed with the customer not to do something?
Dead testing may be useful for ensuring that exposed conductive parts are earthed where it is difficult to disconnect these for Zs testing. In this instance it would be R2 testing and not R1+R2 testing. (Think of a heavy chandelier or whatever.)