I would therefore draw from the IET statement that a complete suite of tests (dead and live) should be done in a domestic situation unless there is good cause not to do so )or for some reason it has been agreed with the customer not to do something?
Only if you ignore the statement in GN3 that cpc continuity can be verified through live loop testing. Dead testing for cpc continuity is designed to ensure that the installation is not energised with unearthed parts. This caution is no longer necessary when the installation is already energised, as any potential danger already exists.

Dead testing may be useful for ensuring that exposed conductive parts are earthed where it is difficult to disconnect these for Zs testing. In this instance it would be R2 testing and not R1+R2 testing. (Think of a heavy chandelier or whatever.)
 
Just to explain. I gave you a 'disagree' about this post. It's nothing personal (honestly) but how anyone can maintain a viable business at those sort of rates I really dont know.

In this part of the world I'm considered to be middle of the road on pricing as far as I can tell.

I don't do many EICRs because normally it's a full day around the £240 mark. Most people are getting them in 2/3 hours for £80-£120. I can't compete with that because I like to be thorough so I can sleep at night.

In this case it's a bit of a favour for a forum member who needed one quick, so I figure karma will pay me back at some point in the future :)
 
What dead tests would you carry out during periodic inspection and testing? Insulation resistance is the only one I would do (assuming that the installation could be de-energised for the test) and would not be with individual circuits but the installation in parallel as required by BS7671. I don't see any reason to be disturbing connections in the DB - although I would be checking tightness of terminals.

Correcting any defects is not the purpose of periodic inspection and testing and is not something I would do. It would be quoted separately as a completely separate job.

Firstly I was commenting in the context of the thread 'domestic' so I have very rarely ever seen a reason not do a full compliment of tests, I would though agree that commercial and industrial can be somewhat of a challenge if they are a mess and this would impact on testing time thus I would discuss with the customer but domestic is seriously not going to be a big issue of putting the cores back in the correct order once you have tested.

How would you ensure without removing cpc from its terminal that one is not picking up parallel paths?, when doing R2 or R1+R2, you are ensuring that the earthing for that particular circuit is not broken, damaged or high resistance etc, measuring ELI when energised only proves an earth path exists but it doesn't confirm the integrity or the circuit earth itself, think boiler supply where an earth path may be present through the pipework itself even if the boiler supply earth was broken.
 
Putting this to bed now guys...thanks for all your assistance and help with my queries, you have been complete pros even essex and buzz who took time out to patronise me :), all the best.
Patronise, eh?.
People seem to jump to conclusions an awful lot. I like to see things from all sides before offering advice on an issue of which I don't personally know all the ins and outs.
There could be much more involved, from both sides. Things look a bit iffy from the contractor's side with the info put forward but the full facts are not known. We are receiving info from a source unknown to us...info which indicates the OP carrying out electrical installation and/or alterations to his own property. Is he competent to carry out this work? Well, it seems not if no initial certificate was produced. He mentions family safety, following the EICR....what about prior to it, following the work carried out?
I am not jumping to conclusions... I've seen plenty 'being led down the wrong path' following such 'leaping'.
By the way, I don't see what trades persons being 'complete pros' has to do with offering free advice.
 
Last edited:
How would you ensure without removing cpc from its terminal that one is not picking up parallel paths?
Certainly there may be parallel paths. However you should remember that you are specifically advised not to unnecessarily dismantle and reassemble the installation as this is more likely to introduce faults than to find them. I would state with absolute confidence that (R1+R2) testing is almost always wholly inappropriate for periodic inspection and testing. (It can be useful if there is no supply - e.g. Economy 7 or a de-energised installation or whatever.)
 
Certainly there may be parallel paths. However you should remember that you are specifically advised not to unnecessarily dismantle and reassemble the installation as this is more likely to introduce faults than to find them. I would state with absolute confidence that (R1+R2) testing is almost always wholly inappropriate for periodic inspection and testing. (It can be useful if there is no supply - e.g. Economy 7 or a de-energised installation or whatever.)

I find it strange that you consider dropping a wire out of a terminal as unnecessarily dismantling the installation, I would consider lifting floorboards up etc is what this little area is covering, otherwise as I have expressed already, how can you ensure the integrity of the earth of a circuit when you can get a false positive through parallel paths, I will agree in certain situations it may be warranted that limitations exists to doing a test but these are the exemptions not the rule.
I was taught to do a full set of tests to ensure the integrity of a circuit and this requires both energised and dead tests for the very reason I have raised about ensuring the integrity of the earth itself and you don't get a false positive, as far as I am aware all the testing guides and advice out there recommends the complete set of tests where possible, I think you are misinterpreting the part about unnecessarily dismantling, unless it has drastically changed then it did once mean pulling the infrastructure and/or fitted furniture apart just to access a joint to give one of many examples... I cannot ever see this applies to removing an Earth or a Neutral from its terminal block, that isn't exactly what I call dismantling the installation.

I will add when you carry out a test and inspection you are assessing the installation and the safety of it, this cannot be done if you do not do the full scope of tests for the reasons given, if you test a shower and the earth is not connected yet your ELI give a pass through a parallel path then you have not identified a very dangerous situation, that is the whole point of the testing and inspection, how can you justify omitting dead tests when you may miss a very real danger, in the scope of this thread which is domestic based then I cannot ever see a real reason to shun dead testing, I have not yet come across a situation where power cannot be removed to do so, commercial and industrial is a different ball park but still it should always be done unless their are exceptional circumstances where power cannot be removed, IE Hospitals IC wards etc...
 
I find it strange that you consider dropping a wire out of a terminal as unnecessarily dismantling the installation
That's precisely what it relates to.

Also (R1+R2) testing will not prevent parallel paths from giving you a reading, e.g. in the case of supplementary bonding.
 
Only if you ignore the statement in GN3 that cpc continuity can be verified through live loop testing. Dead testing for cpc continuity is designed to ensure that the installation is not energised with unearthed parts. This caution is no longer necessary when the installation is already energised, as any potential danger already exists.

Dead testing may be useful for ensuring that exposed conductive parts are earthed where it is difficult to disconnect these for Zs testing. In this instance it would be R2 testing and not R1+R2 testing. (Think of a heavy chandelier or whatever.)

Sorry but we will have to agree to disagree. Your 'quote' comes after that which I stated and is merely a note as part of table 3.4. Table 3.4 states under Ring circuit continuity 'Where there are records of previous test, this test may not be necessary unless there may have been changes made to the ring final circuit'. Why do the GN's then say this if continuity on final circuits is NOT required - as you argue?

I mean no disrespect to you but in my own opinion anyone walking around simply doing Zs testing on final circuits when continuity readings can be taken is only doing half a job unless that is what has been agreed with the customer and the customer fully understands what they are agreeing to with such limitations. The analogy I see is that my garage doesn't just start my van engine and then slap an MOT pass on the vehicle?
 
In this part of the world I'm considered to be middle of the road on pricing as far as I can tell.

I don't do many EICRs because normally it's a full day around the £240 mark. Most people are getting them in 2/3 hours for £80-£120. I can't compete with that because I like to be thorough so I can sleep at night.

In this case it's a bit of a favour for a forum member who needed one quick, so I figure karma will pay me back at some point in the future :)

Thanks for the explanation. Karma restored with a 'like' :)
 
Sorry but we will have to agree to disagree. Your 'quote' comes after that which I stated and is merely a note as part of table 3.4. Table 3.4 states under Ring circuit continuity 'Where there are records of previous test, this test may not be necessary unless there may have been changes made to the ring final circuit'. Why do the GN's then say this if continuity on final circuits is NOT required - as you argue?

I mean no disrespect to you but in my own opinion anyone walking around simply doing Zs testing on final circuits when continuity readings can be taken is only doing half a job unless that is what has been agreed with the customer and the customer fully understands what they are agreeing to with such limitations. The analogy I see is that my garage doesn't just start my van engine and then slap an MOT pass on the vehicle?
I never once mentioned ring final circuit continuity testing. That's not what was being discussed.

However, as you allude to, the Guidance states that where records exist and changes have not been made then it can be omitted.

Personally I would prefer to do end-to-end continuity for ring final circuits to have some indication of continuity - but this would almost always be at a socket outlet rather than ripping a DB apart. I wouldn't be doing the whole figure-of-eight thing without good reason (e.g. if there was particular reason to doubt the ring). If I was going to go to those lengths I would also be looking for additional remuneration.

It really ought to be remembered that we are not "testing" - we are carrying out inspection and testing. Inspection is listed first as it is the most important element of this. The testing is merely to supplement the inspection.

Many things can pass tests which can be seen to be unacceptable and/or unsafe by inspection.
 
That's precisely what it relates to.

Also (R1+R2) testing will not prevent parallel paths from giving you a reading, e.g. in the case of supplementary bonding.

Please cite where it even suggests disconnecting a wire in a dist' board is classed as 'unnecessarily' dismantling the installation, I honestly find this bizarre,it is necessary to do to do the tests, we are taught this method, even if you take a modern testing course now you do all the tests in the usual order, when you did you AM2 test and inspection module would you have failed if you did not do the dead tests as part of the testing routine, I dare say yes, telling the examiner the live test will suffice would be an interesting concept to see what response you got.

In answer to your other point, I take the wire out of the board for dead tests, I will also in the example of a shower, drop the wire out of the shower, this proves the integrity of the cable and the earth wire itself with no parallel paths, I will agree somewhat that commercial and industrial may have circumstances where parallel paths cannot be omitted for testing in all cases but we are on about domestic.

I am open to other views here and will stand corrected if things have changed and I missed that bus but how can one test the actual circuit earthing if you cannot eliminate false positives from energised testing, you simply cannot so you could potentially mark a circuit as safe when it is a dangerous to use, even if your definition of unnecessarily dismantling of the installation was correct, can you not as a professional electrician see the clear danger in this approach that circuits could be unsafe and passed as safe?
 
Please cite where it even suggests disconnecting a wire in a dist' board is classed as 'unnecessarily' dismantling the installation, I honestly find this bizarre,it is necessary to do to do the tests, we are taught this method, even if you take a modern testing course now you do all the tests in the usual order, when you did you AM2 test and inspection module would you have failed if you did not do the dead tests as part of the testing routine, I dare say yes, telling the examiner the live test will suffice would be an interesting concept to see what response you got.

In answer to your other point, I take the wire out of the board for dead tests, I will also in the example of a shower, drop the wire out of the shower, this proves the integrity of the cable and the earth wire itself with no parallel paths, I will agree somewhat that commercial and industrial may have circumstances where parallel paths cannot be omitted for testing in all cases but we are on about domestic.

I am open to other views here and will stand corrected if things have changed and I missed that bus but how can one test the actual circuit earthing if you cannot eliminate false positives from energised testing, you simply cannot so you could potentially mark a circuit as safe when it is a dangerous to use, even if your definition of unnecessarily dismantling of the installation was correct, can you not as a professional electrician see the clear danger in this approach that circuits could be unsafe and passed as safe?
An exam situation is not relevant as they are trying to determine that you know how to conduct all of these tests. That does not mean that they are sensible or advisable when carrying out periodic inspection and testing. This is exactly the over-reliance on testing that I am referring to. An inspection of all the senses is the key part, supplemented by relevant tests as appropriate.

Initial verification and periodic inspection are very, very different beasts. We are not trying to determine whether an installation is safe and compliant to energise as the installation is already energised. What we are concerned with is whether the installation is satisfactory to remain in service.

Totally different thing. Frankly if anyone told me that they did (R1+R2) testing during periodic inspections, my immediate thought would be that they have very little experience of periodic inspection and testing.
 
An exam situation is not relevant as they are trying to determine that you know how to conduct all of these tests.

You make a relevant point that I cannot argue with.

Initial verification and periodic inspection are very, very different beasts. We are not trying to determine whether an installation is safe and compliant to energise as the installation is already energised.

I agree.

What we are concerned with is whether the installation is satisfactory to remain in service.

You still haven't addressed or replied to my main point, how can one determine whether an installation is satisfactory to remain in service when simply doing a energised test to establish a acceptable earth reading could be masking a dangerous circuit if not confirmed with a (R1+R2)
I will also add that doing the R1 +R2 on a socket ring and checking readings at each socket can establish where multiple spurs exist on one spur leg that in itself could be a fire risk, this cannot be determined by energised testing.


Frankly if anyone told me that they did (R1+R2) testing during periodic inspections, my immediate thought would be that they have very little experience of periodic inspection and testing.

I see this at the moment as opinion only, you haven't cited anything to back your position up, also you suggest anyone doing so you make you think they were of little experience, maybe they have been taught differently or are with companies with very different views or methods, I am no longer in a scheme myself as I don't do that kind of work enough anymore, I do however get in a well established local testing company sometimes for the factories that I am on call to to do there Periodic's, they do the dead tests as part of their routine, are you saying they are wrong and inexperienced?
 
What they need to ask themselves is whether they are conducting a test simply because there is a box in which to record a result, or whether they are conducting it for some useful purpose.

In relation to your other point I actually answered it already. I pointed out that (R1+R2) testing is no less at risk of parallel paths than Zs testing.
 
What they need to ask themselves is whether they are conducting a test simply because there is a box in which to record a result, or whether they are conducting it for some useful purpose.

In relation to your other point I actually answered it already. I pointed out that (R1+R2) testing is no less at risk of parallel paths than Zs testing.

Like I also stated as regards to this point, that is easily resolved by disconnecting the earth at both ends and testing the cable, this is not too difficult in the majority of domestic installations to do this with all circuits, this ensures no parallel paths.
Also the box ticking comment, I have given you 2 examples for the need to R1 + R2 a circuit that could be masked by an ELI result giving a false positive, this is how I was taught and the reasons given are the reasons I was taught to always do them where possible.

I therefore don't agree it is a box ticking exercise but a justified test, again I understand there are limitations expecting in commercial and industrial here that I don't disagree about but as is the theme of the thread, 'domestic' warrants a full testing routine imho, I have never heard of or met anyone that thinks otherwise over my career and I have met many contractors well until this conversation.

I still ask in your professional opinion given I have shown you 2 key areas that can be missed in your suggested approach that can leave a dangerous installation marked as safe then do you still stand by your position that it is an optional test, I also would wonder how if someone was subsequently injured or killed with a circuit you had classed as safe yet was shown to be dangerous and would have been picked up had you done the full scope of tests, where do you think you would legally stand. I grant a periodics cannot find everything and this is easily defended in court but actually omitting half the testing may be a little harder to defend imho.
 
I find dead testing invaluable, especially when testing ring finals.
 
Like I also stated as regards to this point, that is easily resolved by disconnecting the earth at both ends and testing the cable
Unnecessary dismantling.

"The purpose of periodic inspection and testing is to provide an engineering view on whether or not the installation is in a satisfactory condition where it can continue to be used in a safe way.

"The periodic inspection and test comprises a detailed examination of the installation together with the appropriate tests. The inspection is carried out without taking apart of dismantling equipment as far as is possible. The tests made are mainly to confirm that the disconnection times stated in Chapter 41 are met, as well as highlighting other defects."

"The tests considered appropriate by the person carrying out the inspection should be carried out in accordance with the recommendations in Table 3.4 and considering sections 3.8.1 to 3.8.4 of this Guidance Note.

"See section 2.6 of this Guidance Note, noting that alternative methods may be used provided they give reliable results." (GN3)
 
Also "Notes:

"4: The earth fault loop impedance test may be used to confirm the continuity of protective conductors at socket-outlets and at accessible exposed-conductive-parts of current-using equipment and accessories."
 
Also "Notes:

"4: The earth fault loop impedance test may be used to confirm the continuity of protective conductors at socket-outlets and at accessible exposed-conductive-parts of current-using equipment and accessories."
I will stand corrected then -

Well if this is what the guidance is advising then it certainly has changed since I did my college back in the eighties, I would still do R1+R2 personally, it shows you potentially dangerous issues that ELI would miss so I still don't agree with the paragraph above, it is noted as number 4: so I may have to look at the surrounding notes to see what context it is presented in, I will also raise a query with the BSI on this matter and see what their input is.
I am still interested in your professional opinion given the scenario I gave can lead to a dangerous situation getting a pass, guidance notes are just that for guidance and I presented you a reason for r1+r2 which I believes justifies it should be undertaken and also made the case that in domestic you can easily and with limited effort do a R1+R2 with parallel paths omitted.
 
I will stand corrected then -

Well if this is what the guidance is advising then it certainly has changed since I did my college back in the eighties, I would still do R1+R2 personally, it shows you potentially dangerous issues that ELI would miss so I still don't agree with the paragraph above, it is noted as number 4: so I may have to look at the surrounding notes to see what context it is presented in, I will also raise a query with the BSI on this matter and see what their input is.
I am still interested in your professional opinion given the scenario I gave can lead to a dangerous situation getting a pass, guidance notes are just that for guidance and I presented you a reason for r1+r2 which I believes justifies it should be undertaken and also made the case that in domestic you can easily and with limited effort do a R1+R2 with parallel paths omitted.
Hi darkwood.
I feel Risteard is just quoting sections out context from GN3 to offer validity and /or substantiate his own view/position on I&T with EICR's. You won't change his view, he is entrenched.

I'd be interested in what his CPS thinks to his opinions, if he is with a scheme.

I'd stop debating with him. He's wont capitulate. I feel he isn't open to a change of viewpoint.

Me; I'm going to start running around domestic installs just measuring Zs values, beats doing it properly :)
 
I was just showing respect, I made my case, showed my position and explained why I hold that train of thought, I showed respect for his views and politely asked in my last post what he thought in his professional stance about sidestepping what I consider important steps in a testing routine because they can reveal dangerous issues that may not be detected by a ELI ... I have yet to receive his answer on that specific question, personally I can't see how one can justify routinely omitting R1+R2 tests given they give valuable info and show dangers up that an ELI cannot.
 
I feel if its initial verification then yes dead tests are essensial, but I don't believe all dead tests are essential in a circuit that has already been energised.
Yes it is good practice, but I have to agree with restart on this one. i was taught in my 2395 ( test and inspect) that earth continuity can be proven by R1 +R2 or wander lead, or just the Zs. It's the inspectors choice.

As for insulation resistance test. I agree it's pretty essensial in an EICR, but as I have stated earlier if I come across a board in such a state as I would have to spend extra time putting it right before continuing, I would not do insulation resistance and mark it as a FI. An inspector is there to inspect, not rectify.

I know we are not discussing minor works hear, but I also quite often dismiss the dead testing on minor works if it's just a light pendant or socket being swapped like for like, however I always do the Zs, RCD 5times rated, and check polarity.
 
I was just showing respect, I made my case, showed my position and explained why I hold that train of thought, I showed respect for his views and politely asked in my last post what he thought in his professional stance about sidestepping what I consider important steps in a testing routine because they can reveal dangerous issues that may not be detected by a ELI ... I have yet to receive his answer on that specific question, personally I can't see how one can justify routinely omitting R1+R2 tests given they give valuable info and show dangers up that an ELI cannot.
It won't show up different to what a Zs test will. Answered this several times already. You are just trying to justify your view so have convinced yourself of the merit. Dead continuity testing is to ensure that an installation is safe to energise. If the installation is already energised then the point is moot. Disconnecting a cpc at both ends is most certainly unnecessary dismantling and can result in it not being reassembled correctly. It's also not how an R1+R2 test is intended to be done. The correct method will not remove parallel paths.
 

Reply to Queries regarding Inspection Report I've just had completed in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
556
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
Our house in a row was built in 1971 and we have metric cables with cpcs for the lighting, top of the row imperial and no cpcs.
Replies
8
Views
1K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks