Well, I say that because I don't think there is a problem other than perhaps my meter reading.

Then again, it might not be a problem at all.

So I had an oil heater that was tripping the RCD. Element was leaking so replaced it.

Also did a complete check of all switches, terminal blocks and cables looking for grounding and all is fine.

Put it all back together, switched it on max and checked the draw on the line with the clamp meter
and it is what I would expect a spot on 10 amps.

So I then clamp the earth cable and it reads 46mA. The RCD is rated 30 mA but it doesn't trip.

Is my meter telling lies or is the clamp picking up the flux from the neighbouring line even though
the line is outside the clamp?

Any thoughts?

Thanks

Ray Pooley
 
From the details on the website you linked to;

200mV/2V/20V/200V (±1.0%), 600V (±0.7%). AC voltage: 2V/20V/200V (±1.2%), 600V (±0.8%). AC current: 2A/20A (±3.0%), 200A (±2.5%), 600A (±1.5%). Resistance: 200Ω/2kΩ/20kΩ/200kΩ/2MΩ (±1.2%), 20MΩ (±2.0%). Requires 3 x AAA batteries.

It's simply not designed to measure current less than 2 Amps with any accuracy. Yes, it will give a reading but the further away you get from the 2 Amp minimum the more inaccurate the reading will be and any reading less than a few hundred miliAmps should just be ignored completely because it's so far outside the design range of the tester. As already mentioned you need an earth leakage clamp meter to give you any meaningful accuracy in the mA range.
 
Clamping the live tails together will give you a better indication of earth leakage.
 

Reply to Question about clamp meters in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top