question about CU with solar PV

Discuss question about CU with solar PV in the UK Electrical Forum area at ElectriciansForums.net

nbhare

-
Reaction score
1
Have not come across a consumer unit with solar fitted before, have been asked to replace the CU, at the moment the CU is a old plastic type with a RCD fitted covering half the circuits, I will be fitting a 17th amm3 CU, now, the question I have is, im presuming the 16A mcb that is currently coming from the solar needs to be fitted independently of any other circuits on its own busbar (because of the disconnection time) but the question is, and excuse me if im being dumb, the power from the solar enters the CU via this MCB, if its not on the same busbar as anything else how can the power be used?

there is a solar Iboost fitted also to the immersion heater/tank, surely if the solar isnt on the same busbar how will the power be utilised by the iboost?

finally, how is the solar MCB treated with regards to testing and filling in the EIC

thanks,
 
So as a learning exercise I had a look about and found a few numbers for "anti islanding" disconnection times. This is the Loss of Mains spec where the invertor recognises that mains has been lost and shuts the invertor down. The disconnection times ranged 0.5 sec to 2.5 sec (didn't sort out why, sorry). It appears this is tested on installation, but there is no periodic test that I found. I understood intention is to protect DNO workers. The householders rely on us to not connect the invertor in a silly way that defeats ADS disconnection times.
 
So has this thread concluded that Solar should never be connected to a CU where the circuit is on a shared RCD or a single pole RCBO?

If so, that means nearly all the solar installations I have come across don't meet the requirements of the regs......
Basically yes.
If connected to an rcbo then the rcbo needs to be double pole.
 
C3EE3CF3-0ABD-4C6F-8705-AC83C66C1B32.jpeg
Or single pole switched neutral?
yes all live conductors require disconnection If an rcd is used for additional protection
 
This thread hasn't been replied to for 14 days, so replying to this one may not get a response. Post a new thread instead.

Reply to question about CU with solar PV in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock