The problem isn't necessarily the loop impedance for the remote end, but what happens if the SWA is punctured shorting line to armour?
Will that cause sufficient current to operate in a suitable time?
I have seen situations where the remote supply (sub board, large load etc) has a suitable Zs due to a core being used as CPC; but the SWA's armour is so poorly connected that a fault to the armour would just pass current forever, or even burn out the connection leaving the armour live.
So the question becomes, would the connection proposed result in a suitable Zs on the armour?
Personally I like to see well over-the-top effort to ensure a solid low resistance connection to all protective conductors be it the cores, or/and the armour.