If it’s a periodic then yes you can use an earth fault loop impedance test as per gn3 to carry out earth continuity, R1+R2 testing is for initial verification but it’s not precluded for periodics if you wish to do it, tho this is nigh on impossible for say an installation which has a metallic Wiring system throughout, say like an industrial application.That is doggy the 1.2 value is only really used for design unless the temperature is stated in the question.
again on 2391-051
and question 23 ignores sequence of tests I know you can have limitations on Periodic inspection but it says to use Earth fault loop impedance test to prove continuity of CPC.
[automerge]1596703388[/automerge]
sorry OP thats not very helpful of me and paper 2391-52 isn't that bad, it's pretty good.
The order of tests for initial verification is not applicable to periodic inspection and testing as the installation has already been in service for x amount of years.