I am trying to carry out live polarity test to test correct polarity of the supply. The system is TN-S and single phase.

My question is do i turn main switch off?

Where on the main switch does the voltage indicator leads go? Is it on the top side of the main switch (Supply) or bottom (Feed)?

Many Thanks.
 
Use an approved voltage tester only....place one probe on the live pole of the incoming supply on the main switch..(normally top),and the other on the neutral....you should get 230v. Now test Live to earth...you should get 230v....now test neutral to earth,you should get 0v....This will verify correct polarity of the incoming supply.
 
Thanks. one more questions please;

Before carrying out the live polarity test the main fuse must be put back and the installation is energised but the main switch is off. Is this correct?

Many thanks again.
 

Reply to Question regarding live polarity test. Please help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
648
462 excerpt below. The incoming supply is via a electrical plant room to the block of flat, each flat has a standard DNO cutout fuse but no...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top