nazoom

Hi

I am trying to carry out Prospective fault Current (PFC) test on a sub board that that is RCD protected and is fed by a main board. My question is how to carry out this PFC (short circuit or earth fault) on the sub board? Do we put the Main switch off in the main board and place the line lead at the line point of RCD that is feeding the sub circuits and then the neutral lead goes on the neutral point of the RCD?

Many Thanks
 
Why? If your PFC/PSSC is in spec for the protective device at the origin, it has to be in spec further down the line assuming that your protective devices in sub board are the same kA ratings as the main board, ohms law. Just calculate it if you really want to record it.

Cheers.............Howard
 
So does that mean that the PSSC/PFC is the same for both the main board and the sub board? And is measured at the Main board?

Thanks.
 
So does that mean that the PSSC/PFC is the same for both the main board and the sub board? And is measured at the Main board?

Thanks.

As stated by Sirkit, its down to Ohms Law. The more ohms between you and the source of supply the less Amps you'll have....SIMPLES
 
the same as if you were doing it at the main board. switch the sub board main switch off with the feed from the main board still on. then measure from the incoming L to N, and L to E at the sub main.
 

Reply to Question regarding PFC on a sub board. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top