Hello all, doing my Part P exam in the morning and feeling confident, so doing a bit of reading up now and ive got the IEE Electricians Guide to Building Reg, and ive come across something which i dont agree with but i may be wrong, the book says, 'A 30 or 32 A circuit is usually appropriate for household or similar cookers of rating upto 15 kW'.
But am i not right in thinking 15000 / 230 = 65 A?????
So 30 or 32 A would be too small???