Question

D

domestic spark

where has this rule come from i have in my head that, all fuse spurs have to be installed in the fabric of the building and cant be, slapped up in units etc
 
Lazy! So ... I looked it up for you.
Elec Guide to Building Regs 5.2.2 (i) should pref be mounted on the building fabric, and not in kitchen furniture.
and BS 7671 :: 530.4.2
 
Last edited:
where has this rule come from i have in my head that, all fuse spurs have to be installed in the fabric of the building and cant be, slapped up in units etc

Kitchen units are normally permanent fixtures even though they are not defined as part of the building fabrication. So imo I have no problem what so ever mounting electrical accessories in practical positions whether this be in kitchen units etc
 