That’s type B, not type A.
My understanding, is that it is charging points for use by the general public which are required to be TT, not those intended for private use.
I think according to BS7671, but it may vary in the COP, type B is only prescribed if the DC residual current is known to be >6mA.
I can find no reference to private individuals being less prone to electric shock:), where does this information come from? I know that apparently private dwellings are apparently less prone to electric shock because of the (possibly soon to be removed) exclusion of PME restriction for a single dwelling.

To doomed, also read Section 722 and ensure the car charging point is a dedicated circuit.
 
@Midwest unless the manufacturer specifically says the charger can be installed on pme without a rod outside then one is needed. even tns needs a rod as trying to get the dno to guarantee there network as not being pme half way down the road is near impossible. you can get away with putting one in a garage where there is no extraneous parts, much likle exporting pme in general. but this will all change come 18th apparently.
I would suggest the OP @Doomed has a look at the EV box stuff, as its better than rolec and if its mounted on a wall then it can have the earth cable fed to the rod via conduit, same if on a pedestal in the car park, run sufficient swa and separate earth back to a suitable spot to sink the rods. As no matter how you install it, if its not on the wall of the building then you are running suitable cable to it, its not much more work to add a correctly sized separate earth cable back to a more convenient spot for the rods.
 
Type A and AC RCDs do not detect d.c. faults. In fact d.c. current is used to prevent them from tripping when using the ‘no trip’ function on MFTs.
6mA d.c. is the maximum current at which type A and AC RCDs will continue to operate.
Type B RCDs detect both A.C. and d.c. current.

The information regarding whether an earth electrode is required can be found in BS7671 section 722.
 
The 18th draft proposal changes to Sec 722 (curtesey IET issue 66) ;

Changes to Section 722
Section 722 (electric vehicle charging installations) provides requirements for the supplies to electric vehicles. There are a number of significant changes in Section 722 of the DPC:

Protection against electric shock
Regulation 722.411.4.1 concerning the use of protective multiple earthing (PME) supply has changed. The exception for a dwelling if none of (i), (ii), or (iii) is reasonably practicable has been deleted. This now means that PME cannot be used unless you meet (i), or (ii), or (iii) of 722.411.4.1. As a reminder of those regulations:

  • Regulation 722.411.4.1(i) refers to a situation where a connecting point is supplied from a 3-phase installation used to supply loads other than charging points and where the load is sufficiently well balanced.
  • Regulation 722.411.4.1(ii) requires a very low resistance earth electrode to mitigate the effects of an open circuit PEN conductor fault on the supply.
  • Regulation 722.411.4.1(iii) refers to protection by a voltage operated device. An important change is that the regulation now makes the point that this device could be included within the charging equipment. It is worth noting that this device will also require an earth electrode.
So whatever POD (my upload) are suggesting, their device will need rodding (if you pardon my expletive)?
 

Reply to quick info on car charging port in the Electric Vehicles Advice Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
515
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

The contacts are pushed open by a cam as the shaft is turned so they operate quite slowly. That's fine on AC as any arc is self-extinguishing at...
Replies
2
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top