Am i correct in thinking that if you did an insulation resistance test part way along a radial back to the CU with it switched on and just the mcb for that circuit tripped that you should get a zero reading between N and CPC (with a TN-C-S supply).
cheers.
 
Am i correct in thinking that if you did an insulation resistance test part way along a radial back to the CU with it switched on and just the mcb for that circuit tripped that you should get a zero reading between N and CPC (with a TN-C-S supply).
cheers.


You would on any circuit or type of supply as the N and E are connected to the star point at the supply transformer

even with the main switch off unless all other circuits are clear readings from these will show on your circ


As the main switch is normally DP then the is no connection between the N and E if switched off.
 
Last edited:
You would on any circuit or type of supply as the N and E are connected to the star point at the supply transformer




As the main switch is normally DP then the is no connection between the N and E if switched off.
what i was saying is if there was a fault on one of the other circs it would show on the one being tested hence why the need to discon the n being tested
 
Does that apply to a TT system as well?

Yes as the path to the transformer is via the consumers earth electrode and the earth electrode at the transformer or how else would you have a path to allow the protective device to operate on a fault to earth?
 
Last edited:

Reply to quick IR test question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top