why would an old house require 100 amps?
I don't know the fuse was already in it. The new board is 100A switch as there's a new shower circuit been put in.
Just because the main switch is 100a doesnt mean you need to change the meter. The rating on the switch is to show its capable of switching 100a safely without welding itself closed/open. As for the shower, check diversity... (appendix 1 of the on site guide)..
New 25mm tails from meter to new consumer unit, but what about the tails from the main cut out to the meter ? Still gonna be 16mm ? Protected by 100A main cut out fuse ? Main cut out to meter needs to be 25mm or fuse needs to be smaller, 60A.Neither of which can be (legally) done by us sparkies.