Greetings.

I apologise if this is a bit of a daft question but I don't know much about three phase.

In a three phase system there is only current in the neutral if there is an imbalance of the phases right?

So looking at the transformer that supplies our street it is a three phase transformer that supplies various houses on different phases.

Each house has a line and neutral so does the above principle mean that the neutral cable in my own house will be carrying less than the phase?

If the current in the neutral cable is a result of an imbalance between the phases then does this principle apply to houses that are supplied from the same three phase transformer?

Any opinions appreciated.

Thanks.
 
you are only using 1 of the phases in your house so there will be no other phases to cancel each other out hence the neutral current will not be lower. probably a poor way of explaining it but hopr it helps
 
Greetings.

I apologise if this is a bit of a daft question but I don't know much about three phase.

In a three phase system there is only current in the neutral if there is an imbalance of the phases right?

A perfectly balanced load, eg a motor, no Neutral Current, hence no N conductor.

So looking at the transformer that supplies our street it is a three phase transformer that supplies various houses on different phases.

Each house has a line and neutral so does the above principle mean that the neutral cable in my own house will be carrying less than the phase?

If the current in the neutral cable is a result of an imbalance between the phases then does this principle apply to houses that are supplied from the same three phase transformer?

Any opinions appreciated.

Thanks.

As for the rest, I assume, house will just be spurred off the the street cable, so your house L & N currents will be equal.
Overall I should imagine there will be an imbalance across the 3Ps, so there will be a N current.

Then you've got Harmonics!!!

At this point I'll gracefully bow out and leave it to the Forum superiors! :)
 
Not sure what you are asking here La Poste, but if you have three houses in your street, each supplied from a different phase, the load at each house would have to be identical to have no neutral current at the 3 phase transformer. the loads would be different of course, how you would calculate the neutral current at the transformer, especially if you had a long row of houses is a whole another question.
 
Not sure what you are asking here La Poste, but if you have three houses in your street, each supplied from a different phase, the load at each house would have to be identical to have no neutral current at the 3 phase transformer. the loads would be different of course, how you would calculate the neutral current at the transformer, especially if you had a long row of houses is a whole another question.

Neutral curent is given by:

In=√(Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic))
 
Thanks people that's food for thought.

As for the rest, I assume, house will just be spurred off the the street cable, so your house L & N currents will be equal.
Overall I should imagine there will be an imbalance across the 3Ps, so there will be a N current.
Then you've got Harmonics!!!

So there are two elements to this neutral current, one is the neutral current from each house which will be equal to the phase current as they are single phase and the second element is a neutral current due to imbalances of the three phases that you call Harmonics.

Would it be fair to say that sometimes the current in my neutral will be larger than my phase current?

I'm in dark territory here but it bugs me that I don't understand.
 

Reply to Quick three phase question in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
886
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top