Greetings.

I apologise if this is a bit of a daft question but I don't know much about three phase.

In a three phase system there is only current in the neutral if there is an imbalance of the phases right?

So looking at the transformer that supplies our street it is a three phase transformer that supplies various houses on different phases.

Each house has a line and neutral so does the above principle mean that the neutral cable in my own house will be carrying less than the phase?

If the current in the neutral cable is a result of an imbalance between the phases then does this principle apply to houses that are supplied from the same three phase transformer?

Any opinions appreciated.

Thanks.
 
Neutral curent is given by:

In=√(Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic))

I think I get that...

In a perfectly balanced load (Ia² + Ib² + Ic²) will be equal to ((Ia x Ib) + (Ia x Ic) + (Ib x Ic)) so they cancel each other out.

So if you had 10A on each phase you'd get...

In = √(10² + 10² + 10²) - ((10 x 10) + (10 x 10) + (10 x 10))
In = √(100 + 100 + 100) - (100 + 100 + 100)
In = √300 - 300
In = √0
In = 0A

but if Ia was 20A for example you'd get...

In = √(20² + 10² + 10²) - ((20 x 10) + (20 x 10) + (10 x 10))
In = √(400 + 100 + 100) - (200 + 200 + 100)
In = √600 - 500
In = √100
In = 10A

Is that about right??
 
Back to simplicity;

3 phase / neutral cable down the street.
Each house has only a 3kw load switched on.
Live and Neutral current at each house is equal (give or take a harmonica)

Last house is Red, no not paint, L1.
Neutral in the 3ph cable= same current as L1.

Next house back is Yellow, your lucky I didn't say white, L2
Neutral in the 3ph cable = less than the total of the L1 + L2 so far.

Next back is Blue, lost for words, L3
Neutral current in the 3 phase cable = 0
 
I think I see it.

Within each house the line and neutral currents are the same but when the neutral cable hits the main drag (the three phase neutral cable) this is when things start to cancel out.

And the overall current within the three phase neutral cable will be equal to Tony's equation above.
 
Simplistic as it might sound, draw a simple line diagram, think where the currents are flowing, apply Kirchoff's Law, and ALL will be revealed! Await that moment of enlightenment. :)

You'll be (and I have been many a time) amazed how relatively simple it is in the end.
 
I think you should retake maths.
If you want to be pedantic:

In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

Which is how it has to written in Excel!


Or

In=√((Ia²+Ib²+Ic²)-(Ia*Ib)-(Ia*Ic)-(Ib*Ic))

Tony, not being pedantic.

As you know a 0 makes abig difference to the answer, same as where you put a bracket, or a decimal point or a SQrt sign.
 
Or

In=√((Ia²+Ib²+Ic²)-(Ia*Ib)-(Ia*Ic)-(Ib*Ic))

Tony, not being pedantic.

As you know a 0 makes abig difference to the answer, same as where you put a bracket, or a decimal point or a SQrt sign.

They are both correct, its just 2 different ways of coming to the same result, admittedly Tony's excel version is more complex on the eye but still correct.
 
Tony's original post is incorrect.

Thats why I raised it.

He has subsequently corrected the formulae in the last post.

Yes missed that post thought they all were same... missing outer brackets thus give Sqr root on first bracket result only as appose to total bracket equation.

Not like Tony though i must say but he has corrected it :thinking2:
 
[ElectriciansForums.net] Quick three phase question
Originally Posted by Tony [ElectriciansForums.net] Quick three phase question
Neutral curent is given by:

In=√(Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic))



lol I learned that equation recently



Bruce, thats the wrong formulae.



[ElectriciansForums.net] Quick three phase question
Originally Posted by Moses [ElectriciansForums.net] Quick three phase question
Or

In=√((Ia²+Ib²+Ic²)-(Ia*Ib)-(Ia*Ic)-(Ib*Ic))

Tony, not being pedantic.

As you know a 0 makes abig difference to the answer, same as where you put a bracket, or a decimal point or a SQrt sign.



This the correct one.
 

Reply to Quick three phase question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top