where would i find this in the red book?

The correction factor for cables installed in free air with 70oC thermosetting insulation and an ambient temperature of 50oC is?

any help would be much appreciated,

regards
 
this is wat is confusing me, it says 70oC thermosetting insulation. the tables has "70oC thermoplastic" and "90oC thermosetting" so which one do i look under?

heres another one, too

The correction factor for cables installed in free air with 90oC thermosetting insulation and an ambient temperature of 40oC is

A: 0.76
B: 0.69
c: 0.96
D: 0.86
 
Last edited:
The new table 4B1 is more limited than the old one.

I think the first questioin may have been a typing error - not unusual for C&G).

Your second question doesn't have the right answer - should be 0.91 - again another C&G error, but I think you copied it incorrectly as only one of the 4 answers (0.76) is a possible answer. They will only list 4 figures which you could get from the table.

However, you can get 90deg thermoplastic and 60deg thermosetting which the table doesn't address.

You need to just go on the temperature rating of the cable, not what it's made of.

The rating factor will allow enough current to heat the cable up to its maximum temp.

So if you have a 90deg thermoplastic in an ambient of 70deg then the rating will be 0.58 which will get it to 90deg

P296 gives ratings and factors for 60deg and 90deg flexible cords whether thermoplastic or thermosetting

Mike
 

Reply to Quicky - 2382 question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Similar threads

  • Question
As above, for each segment of a complicated arrangement you use the lowest cable temperature rating of that group in any CCC computation. Zs it...
Replies
4
Views
712
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top