Re: R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions

The test you do for a RCD is what you have done with a calibrated RCD test instument.

If all you tests are good then you have nothing to worry about.

Touching the CPC and neutral is not a test ,Wirepuller has covered this.
 
Re: R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions

So why do you think this has caused rcds to trip in the past tony?
 
Re: R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions

Touching N & cpc together will only trip an RCD if there are leakage currents from other circuits on the cpc.
 
Re: R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions

Cheers makes sense as only had light on in bathroom.
 
Re: R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions

What you are thinking of is a neutral to earth fault on a circuit that trips the RCD ,ill try and explain ,as the guys have said there is no inbalance between the L and N , way to look at it is like a perfectly balanced set of scales and the center being the cpc so anything that upsets the balance trips the RCD if you have isolated the supplies and the RCD didnt trip its as has been said no inbalance due to there being no current flowing how ever if the cables are grouped they can get an induced electric field in the cable though it being small could cause the RCD to get an in balance thus tripping the RCD
 

Reply to R.c.d fault????? Rcd not tests fine but does not disconnec under fault conditions???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Very technical :D
    • Like
Replies
9
Views
565
Cheers guys. I was working on the same assumption, but was aware for MF the wagos in wago box were derated 32s, and couldn't find anything to...
Replies
7
Views
350

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top