the operating current of the rcd is irrelevant for the 1xtest, it should still trip in <200/300mS whatever the rating. all you need to alter is the test current on your test equipment. i.e. 10/30/100/300/500/1000mA.
 
Rcd test for a 30ma trip
Is 1/2 15ma current should not trip
1x 30ma current should trip before 200milli secs
5x 150ma current should before 40milli secs
That is for 16th edition
So for 100ma rcd you still use 1/2 x 1x 5x
 

Reply to r.c.d. tripping times ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

  • Question
I would have to say that something is wrong with the light. I would advise to get an electrician. Good luck
Replies
1
Views
292
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
813

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top