when testing R1+R2 should the cpc be taken out of the earth bar and linked to the phase condutor? The reason I am asking is because my supervisor is complaining that my R1+R2 readings are higher than Zs readings, this is due to parrallel paths (conduit wiring system). So should I leave the cpc in earth bar so that these paths are included in R1+R2?
Thanks
 
all depends on whether or not the conduit is your cpc
 
Last edited:
R1+R2 is a measurement of the resistance of the line and cpc conductors only and shouldn't include any parallel paths.
 
Be aware to make sure though that you disconnect the earth from the back box to the socket plate as this will give you paralel earths especially if it's in conduit

I think this is the basis of his original question.

If he disconnects from the earth bar then there can't be any parallel paths. The meter will only be reading the resistance of the line and cpc.
 
Thanks for everyones input, I just wanted to clarify that I was right to carry on testing and recording as I have been before being questioned about my readings. Due to the installation (large commercial install) there are so many paths to earth so every circuit on this DB has a higher R1+R2 than Zs
 
jud what i meant to say is if the conduit goes back to db and the flying earth lead from back boxes is still connected even if you take earths out of earth bar at board and link testing at sockets for r1 r2 you will get a false reading as the conduit is acting as earth as well
 
jud what i meant to say is if the conduit goes back to db and the flying earth lead from back boxes is still connected even if you take earths out of earth bar at board and link testing at sockets for r1 r2 you will get a false reading as the conduit is acting as earth as well

No it won't.

The conduit will no longer be part of the circuit under test as it doesn't form part of the loop i.e the resistance down the line conductor to the link in the DB and back up the cpc to the other test lead is all that the meter will read.
 
Jud if the containment is conduit and it's tubed back to the board this is an earth path if you disconnect live and eart at db and link you then test at sockets or light switch etc if there is a flying lead from socket or light switch etc to the back box it need to be disconnected as this will give you a parralel earth path ie a false reading
 
Yes it is a parallel path when the cpc is connected to the earth bar because the earth bar is linking the cpc and conduit together and making it one loop.

Think of it this way....

Take a length of wire. Strip both ends and also strip a section of the insulation from the middle (this simulates the cpc connected to the back box at the socket). Take a reading from the middle to one end and record the result. Now link both ends of the wire together (this simulates the cpc and conduit connected together in the earth bar) and take a reading from the middle to the link and you'll get a lower reading i.e parallel paths.

If it helps try drawing a picture.
 
Last edited by a moderator:
Done the above test many times jud and tried the tests with and without flying lead to back boxes with the flying lead connected you get a much lower reading now what is that telling me it's picking up other paths or have I been doing these tests all wrong
 
Thanks for everyones input, I just wanted to clarify that I was right to carry on testing and recording as I have been before being questioned about my readings. Due to the installation (large commercial install) there are so many paths to earth so every circuit on this DB has a higher R1+R2 than Zs

I reckon you are doing it right and it is quite worrying that your supervisor doesn't understand how parallel paths affect Zs measurements. Perhaps you need to suggest he does his 2391 again.........
 

Reply to R!+R2 Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top