hi guys and girls,
any ideas on why when cunducting an R1 and R2 and also polarity when it was a closed circuit i had 1.87 ohms but when opened circuit 238ohms. this was on a lighting circuit pme system all correctly main bonded and zs complied.
thanks
 
Was the main switch still on at the CU? If there were other lights in the circuit with their switches "on" then the measuring current can run from the CPC through the N-E connection up the neutral through the light bulb and back to your line conductor, then you are measuring the resistance of the light bulbs "on" in the circuit.
 
yes, it was just that circuit i was working on so just that circuit isolated. it was a tidy job before me, they looped the live out the com in a 2gang switch then used the earth as a switch live, then at the ceiling light connected the earth to a single and ran it to the wall light's. all earth's cut off on class 1 fittings. been like it years he said. been put right now.
 

Reply to R1 and R2 parallel earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Maybe the OP can clear up something. Is there a CPC in the form of the cable armour? If so then it might not be practical to isolate it at the...
Replies
7
Views
4K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
Hi everyone. There is no boiler etc or spur on circuit I can confirm. When testing I did use the plug top attachment lead. I added 4 new Mk twin...
Replies
7
Views
1K
For most domestic work the "standard circuits" in the On-Site Guide Table 7.1(ii) are all pre-checked for adequacy in these aspects, also there is...
Replies
3
Views
1K
  • Question
Correct. For TUNGSTEN FILAMENT (INCANDESCENT) LAMPS: Total power of fixture: 20x 2W lamp = 40W. Total current needed by fixture: 40/230 = 0.17A...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks