Hi, when testing R1 and R2 do you measure from the incoming live to earth or switch live to earth, thanks
link at the board its safer by disconnecting at the db you wont accidentally leave a link on out in the field and turn the supply back on boom
Also R1+R2 is supposed to bejust a measurement of the conductors of the circuit, not including any parallel paths, which there could very well be if a link was used to the earth bar.
I think i know what you are referring to!!
When testing R1+R2 at pendants, you test from the earth terminal to the switched live, with the switch turned to the on position. So that way you are also testing both sides of the switch drop.
yes that is what i ment thanks as i was getting 2 different readings at the pentant on a lighting circuit and wondered which one was correct.
Reply to R1 and R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
No worries.
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
OLDBOY
O
Did you ever find the fault? We like updates 😀
I have a set. I must admit that I seldom use them however. But the concept is good in my opinion.