hello
1.is that acceptable if i do only Zs test last point of the lighting circuit and on scoket!
instead of measure R1+R2?
i can caluclate R1+R2 ACTUALY!
ZS-ZE=R1+R2 is it acceptable to write the value on certificate?

2. as i know the maximum Zs by rcd (rcbo)protected circuit 1667 ohm!
but if the measured circuit is wery high value ,but not reach 1667 ohm ,then is it still acceptable ?

IM new to testing learning currently!
 
I was always under the impression that summing Ze plus R1+R2 is an acceptable method of establishing Zs.

However, doing the reverse and subtracting Ze from Zs to determine R1+R2 is not acceptable practice.

Agree on the accuracy point above, I'm increasingly finding that no trip Zs tests are giving strange readings when lots of LEDs on ccts, though I'm running an older tester.
 
but in new installation is acceptable?for initial verification!
mi right?
Hi - apologies if I've misunderstood your post, but for initial verification this is a dead test. We measure R1 and R2 (and other things :)) prior to energising the installation. I take this from Regs 643.1 and 643.2.1 .
 
agree with most. on a new installation, or part thereof, no circuit should be energised until after dead testing , inc. R1+R2, has been carried out to ensure that the circuit/s is/are safe to energise.
 

Reply to R1+R2 and Zs calculate acceptable? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
263
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top