First and foremost you're supposed to identify parallel paths and where possible remove them for testing purposes only - so you get a proper reading.
Agreed, though on lost of industrial/comercial you wont have much choice.
I don't agree that recording an incorrect and unreliable value as opposed to a tick in that situation would be the correct way to fill your cert in. But thats just my opinion. Each to their own.
The tick is there to verify continuity wher the reading is not reliable due to paralell paths for example.
My view on the 'tick' is that you're ticking to confirm that you've done the R1+R2 and that the reading isn't reliable.
Agreed
Mark.
If the reading is unreliable then it is a fail.
My company just zs everything and calculate. Zs-Ze theres your r1+r2 i dont necessarily agree with this but for ÂŁ25 for an intial test and inspect why not. Some mug countersigns everything and he has got the NICIEC stamp to his name so he is in the dock. Its wrong but sadly my company is quantity not quality they practically let anyone test as long as the figures vaguely look right. I guess if you IR okay and your Zs values seem legit its not that bad but it should be measure first and calculate if you cant power down. Regs cover you for both methods. Needless to say i am looking to move on.....
r1+r2 isn't the same as R1+R2 so i hope this is a typo lol.
Yes, your company is wrong - bad practice and you're doing nothing but sucking pennies off unsuspecting customers. You're right, the 'mug' that signs it off will be in trouble one day if **** hits the fan. Unfortunately, people get away with this type of behaviour because nothing goes wrong. But if it ever did....
by doing R1+R2 you're confirming the earth is continuous before you make the installation live, so to calculate this is beyond stupid in my eyes.[/QUOTE]
In the case of an EICR which is the subject of the thread the installation is already live.
See post #25 which gives the correct information.
if its an eicr on an existing property then calcing it is fine as long as tye circuit was working properly before hand.r1+r2 isn't the same as R1+R2 so i hope this is a typo lol.
Yes, your company is wrong - bad practice and you're doing nothing but sucking pennies off unsuspecting customers. You're right, the 'mug' that signs it off will be in trouble one day if **** hits the fan. Unfortunately, people get away with this type of behaviour because nothing goes wrong. But if it ever did....
by doing R1+R2 you're confirming the earth is continuous before you make the installation live, so to calculate this is beyond stupid in my eyes.[/QUOTE]
In the case of an EICR which is the subject of the thread the installation is already live.
See post #25 which gives the correct information.
afterall you cant take a zs with no earth
if its an eicr on an existing property then calcing it is fine as long as tye circuit was working properly before hand.
afterall you cant take a zs with no earth
Miraculously I've seen a Zs for lighting circuits with no CPC appear on certificates on more than 1 occasion. :banghead:
then its probably been made up from the van.Miraculously I've seen a Zs for lighting circuits with no CPC appear on certificates on more than 1 occasion. :banghead:
if it was tested 2 lead method on no-trip they wouldn't get a reading would they
You most likely find that if the result wasn't made up in the van it was most likely R1-Rn measured.
I have this in the back of my mind that the NICEIC issued guidance on lighting circuits that don't have CPCs in one of their docs. It was about class II accessories and board changes, and also dealt with the testing. part as well