An experianced tester when carrying out an R1R2 test will have a rough idea of what results to expect , some times when you do a test you can get a high R1R2 and when you carry out a Zs test you get a lower Zs reading than you should get ,this could be due to parrallel earth paths, so realistically you should do a dead R1R2 test at more than one point ,because if your last point is on the bathroom lighting circuit and it has a supplimentary bonding conductor from the light to a shower as it should be to 16th ed then the reading you could get would be incorrect due to the paralle earth path , how ever this should be disconnected prior to the Zs any way , im a firm beliver in doing it properly R1R2 ,IR,Zs,RCD,Ramp , than you know your readings are correct