If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
OK lets take some actual numbers, Ze or Zdb .22, on the ring Live .45. CPC .76 So 1.21 / 4 = .30 That figure is only used to check around the RFC for higher than expected readings It goes nowhere on the cert, what does go on the cert is the sum of ZE & R1+R2 which is 1.43 which is Max measured ZS only its not, its theThe r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer
I understand but can you explain this, its from an example eicr in a well know textbook R1 .46 R2 .76 r1+r2 = 0.08 ? with a max measured Zs of .37No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
It's plainly written down in GN3 and other readily available publications. can you tell me the pageThe r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.