the pict

-
Mentor
Joined
Dec 30, 2010
Messages
1,194
Reaction score
292
Location
Brodick
We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
 
We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
 
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
OK lets take some actual numbers, Ze or Zdb .22, on the ring Live .45. CPC .76 So 1.21 / 4 = .30 That figure is only used to check around the RFC for higher than expected readings It goes nowhere on the cert, what does go on the cert is the sum of ZE & R1+R2 which is 1.43 which is Max measured ZS only its not, its the
sum of the readings, to get a measured ZS its a live test done at a socket as that is the only real result . However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer
 
However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer

No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
 
If you have measured all tests correctly on a ring final circuit & checked the r1 + r2 /4, you will have all the necessary check sums & measured results ( Ze, Zs Zdb) to fill out the cert. So whats the problem ! Maybe( R ) Stands for Radial !
 
No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
I understand but can you explain this, its from an example eicr in a well know textbook R1 .46 R2 .76 r1+r2 = 0.08 ? with a max measured Zs of .37
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
It's plainly written down in GN3 and other readily available publications. can you tell me the page
 

Reply to R1 R2 Chestnut time again in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If the plug works in most sockets but not one, then the socket has a problem. If the plug is out of spec as nasty fake one, or been bent by abuse...
2
Replies
15
Views
1K
I have an "old school" electricity monitor similar to this one...
Replies
3
Views
208

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc