R1 + R2 does not equal (R1+R2) in example in On Site Guide. | Page 2 | on ElectriciansForums
Discuss R1 + R2 does not equal (R1+R2) in example in On Site Guide. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
r is for ring
R is for resistance
R1 + R2 is the resistance of the earth and line of the circuit connected together
but if you do add r1 and r2 together and divide by 4 you should get R1 + R2 in theory
Due to parellel Earths though you may not get a text book reading
As stated R and r are completely diferent
clear to me, but you couldn't of read GB£ page 100 note 13 Is that clear?
Yes but col. 13 IS R1+R2.
He was wondering why cols. 10 (r1) and 12 (r2) do not add up to col 13 because he mistakenly called them R1 and R2.
As I wrote, mine do as they ARE R1 and R2 not r1 and r2.
Col. 11 (rn or Rn) is incidental but the same.
Is that clear?
I have found it in the BGB.
You mean measuring from a spur would make R1+R2 more than (r1+r2)/4.
That would be true but I still think you have missed the point of the OP and my comments.
I have always been a bit confused about boxes 10,12 and 13 in the example of a completed 'Form 4 - schedule of test results'.
I understand why the value we get for R1+R2 (when measured at a socket) is a quarter of the end to end resistances, but why on the form is this not more clear?
Box 10 (R1) and Box 11 (R2) do not equal Box 13 (R1 + R2). Again I understand why, but it just seems wrong to have a box for R1 and a box for R2 but adding them together is not R1+R2.
Its annoying :cuss:
The form is correct as boxes 10,11 and 12 are asking for the end to end resistance for r1 , rn and r2 , these are all end to end resistances as in step 1 of the ring final circuit test to check that they are substantially the same , the true R1 + R2 of the circuit is established in step 3 by cross connecting R1 and R2 and measuring at each socket outlet this goes in box 13 . If you add up box 10 and 12 and divide by 4 this cross references your R1 and R2 .
It's really quite simple, if doing an EICR the installation has power so only need to do end to end to make sure it's a ring then do. ZS at each socket. If no power then you have to do R1+R2 and work out ZS by adding it to ZE.
Reply to R1 + R2 does not equal (R1+R2) in example in On Site Guide. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net