Testing R1/R2 on 10mm/4mm T&E cable and the reading is 0.00? Never had this before, can I record 0 on the cert?
 
Checked leads,nulled before testing,took one croc off and tested open circuit put leads on and put testers in hands free then operated the isolator switch in the circuit and it switches between 0 and open circuit...it’s about 8 mtrs max cable run,
 
Yes that was my concern I can’t record 0,the testers are calibrated and the batteries are fine it’s brand new 10mm cable...is there any percentage or tolerance +/- on R1-R2?
 
Never thought of doing that,thanks grant,using kewtech kt63 if that helps never had any issues before with it...

I'd put it down to calibration error combined with your meter's accuracy. Looking at the spec, you've +/- 2 digits on continuity, meaning if it was perfectly calibrated and you were measuring a known resistance of, say, 0.05Ohm, the reading could be anything from 0.03 - 0.07 Ohm. It's what happens when trying to take measurements at the bottom end of the scale.

Record it as 0.01, or if you know how long the cable actually is, work it out from the tables.
 

Reply to R1+R2 of zero zilch nothing?...... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
448

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top