Discuss R1+R2 of zero zilch nothing?...... in the UK Electrical Forum area at ElectriciansForums.net
Are you doing the testing correctly?Testing R1/R2 on 10mm/4mm T&E cable and the reading is 0.00? Never had this before, can I record 0 on the cert?
Thinks so,R1-R2 joined at board, disconnected at appliance, leads nulled, switch closed,croc on R1 croc on R2 test? Got Ze of 0.18 on tncs previous...Are you doing the testing correctly?
Never thought of doing that,thanks grant,using kewtech kt63 if that helps never had any issues before with it...Could be to low for your tester. Test it with out the leads nulled then deduct the test lead resistance off afterwards
What scale have you set on your MFT?Thinks so,R1-R2 joined at board, disconnected at appliance, leads nulled, switch closed,croc on R1 croc on R2 test? Got Ze of 0.18 on tncs previous...
Exactly what I was going to askWhat scale have you set on your MFT?
Never thought of doing that,thanks grant,using kewtech kt63 if that helps never had any issues before with it...