Just installed a small length radial circuit. Total length from board no more than 2 meters. Halfway along is a FCU and a double socket at the end. Linked line and earth and tested at the socket and got a R1 R2 reading of 0.10 ohms,hit the switches to confirm polarity and the reading stays the same. Am i missing something here? surely i should loose continuity and the meter should go full scale, just like when testing R1 R2 on a lighting circuit? Am i having a proper brain freeze moment here??
 
exactly my point
The OP may have realised his error, if we are correct, which seems likely, but there is no shame in making a mistake we all do it, it's how we learn, I hope he comes back and puts our minds at rest, certainly not going to take the proverbial out of him.:)
 
I was using the plug in tester and was getting silly high readings even after nulling, hence why i dropped the socket front and tested at the screws. Of course i wont get any break in continuity testing at the back..... As Cpt Mainwaring used to say..... Time to get a new plug in adaptor i think.
 
I was using the plug in tester and was getting silly high readings even after nulling, hence why i dropped the socket front and tested at the screws. Of course i wont get any break in continuity testing at the back..... As Cpt Mainwaring used to say..... Time to get a new plug in adaptor i think.
Good man
 
Can i just ask one more thing? Why do you guys not like the idea of a double socket fed from the fcu? The garage door from the fcu is only a 50w motor.

Fluke 1652c
Have you taken the supply to the socket from the load side of the FCU? The ideal way of doing you circuit, would be feed from CU to socket, FCU to feed door motor suitably fused down,not the way you have configured it.
 

Reply to R1 R2 on Radial circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
932
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top