Hi
Quick Question about calculations, if we have a ratio between 2.5mm cable and 1.5 mm cable how can i calculate either R1 or R2 from a (R1+R2) value.
if i use a common denomenator method i.e. 5 / 8 where 0.5 is the greatest denominator then x 3 for 1.5 mm and x5 for 2.5 then the resistance of the cpc (1.5) is much lower than that of R1 but given the CSA of the 2.5 is larger i'd expect that value to be higher
hope this makes sense
don't make sense to me. the ratio for 2.5/1.5 is 1.67. i.e. R2=(R1x1.67). for other ratios, the value of R2 is determined by the ratio of the csa of each conductor.
To be honest Hi Ho it does not make a lot of of sense to be honest.
The ratio between 2.5 and 1.5 mm cable is 2.5/1.5= 1.67. Therefore your 1.5mm cable will have a greater impedance as the CSA is smaller. An example would be a 2,5mm of 0.54 ohm, the same length of cable in 1.5mm would be 0.54*1.67 = 0.90 (rounded)
If you devide 2.5 by 1.5 you get a factor of 1.67
Therefore if your 2.5mm cable measured 0.03 Ohms, I would therefore expect 1.5mm cable to have 1.67 times more resistance (0.03 x 1.67) = 0.05 Ohms
I hope this is the question you asked.
Is this what your after Hi Ho
Courtesy of Widdler copied from a previous post hope it helps!!
RT represents the total, in this case, the R1&R2.
A1 is the CSA of R1, and A2 is the CSA of R2.
For example... say you have an R1&R2 of 0.85ohms and you want to determine R1, Rn and R2. In theory we can determine Rn from obtaining R1's value.
So..
R1&R2 = 0.85 ohms..
R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5) = 0.53 ohms
R1 = (RTXA2)/(A1+A2) = (0.85x1.5)/(2.5+1.5) = 0.32 ohms
So we have (R1) 0.32 ohms + (R2) 0.53 ohms = 0.85 ohms (R1&R2)
It works out the other way round - swap the multipliers.
x3 for the 2.5 and
x5 for the cpc.
e.g. R1=R2 = 0.8
0.8 / 8 = 0.1
therefore R1 = 0.1 x 3 = 0.3 and
R2 = 0.1 x 5 = 0.5
I add together the two CSAs, divide the R1 + R2 by the total, and then multiply that by the CSA of the other conductor to the one I wish to determine.
Using Tony's value of 0.85.
2.5 + 1.5 = 4
0.85 / 4 = 0.2125
0.2125 X 1.5 = 0.31875 = R2
0.2125 X 2.5 = 0.53125 = R1.
2.5 + 1.5 = 4
0.85 / 4 = 0.2125
I think that's the way tony mc has explained it. :shades_smile:
I add together the two CSAs -- R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5)
divide the R1 + R2 by the total -- R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5)
and then multiply that by the CSA of the other conductor to the one I wish to determine -- R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5)
2.5 + 1.5 = 4
0.85 / 4 = 0.2125
something amiss there, you get R1>R2.
my way:-
R1+R2=0.85
R1+ (R1x 1.67) = 0.85
R1 x (2.67) = 0.85
R1 = 0.85/2.67 = 0.318
R2 = 0.85 - 0.318 = 0.532
2.5 + 1.5 = 4
0.85 / 4 = 0.2125
0.2125 X 1.5 = 0.31875 = R1
0.2125 X 2.5 = 0.53125 = R2.
Only a misprint
R1 + R2 Ratios
Australia
TETPV,
telectrix,
TrueNAS JBOD Storage Server