R1+r2 reading and r1,r2 and rn on ring final | on ElectriciansForums

Discuss R1+r2 reading and r1,r2 and rn on ring final in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

Abu

Hi there
Been stuck on this for a while. What is the maximum r1+r2 reading possible on a lighting circuit in a domestic property. With a type b 6amp breaker.
Also if you guys could tell me about r1+r2 and rn Maximum readings for ring final.
Thanks
 
Zs = Ze + (R1 +R2) - so you know the Ze, then then you can calculate the R1 + R2 value, then look up the rest in the books

As for a ring - what do you understand about the configuration of a ring and how you would test it?

What are you trying to achieve?
 
Hi there
Been stuck on this for a while. What is the maximum r1+r2 reading possible on a lighting circuit in a domestic property. With a type b 6amp breaker.
Also if you guys could tell me about r1+r2 and rn Maximum readings for ring final.
Thanks
It's R1+R2 r1, r2 and rn are the end to end resistances of the L, N and CPC R1+R2 is the reading obtained by the figure of 8 test
 
It's R1+R2 r1, r2 and rn are the end to end resistances of the L, N and CPC R1+R2 is the reading obtained by the figure of 8 test
Yes i understand and know how to measure it ut was wondering what is the maximum value allowed for the test
 
For electrical certification you can only calculate Zs ,Ze and R1 + R2 are measured using test equipment. If you have a Ze then you can have a designed R1 + R2 based upon the chosen installed cable. Therefore designed Zs from that you can choose a protective device from the tables in BS7671.
 
If you have the On Site guide then in table 7.1 in chapter 7 this lists the maximum length of cable permitted for standard circuits in various installation methods and with different protective devices.
Then you can compare the circuit lengths with the resistance values given in appendix I to give you maximum values for resistance.

For instance a 2.5/1.5 ring final circuit on a 32A MCB with 30mA RCD protection has a maximum length of 106m. (this is limited by voltage drop)
Therefore on 106m your r1 and rn would be 0.00741*106 =0.785Ω
your r2 would be 0.0121*106=1.28Ω

Similarly for a 1.0/1.0 6A lighting circuit the max length is 59m and so R1+R2 would be 0.0362*59=2.14Ω.
 
Measure the ring final circuit readings i got a ze of o.14 at db on tns system i got a reading of 0.55 for r1 +r2 i would like to know what is the maximum reading allowed .
 
If you have the On Site guide then in table 7.1 in chapter 7 this lists the maximum length of cable permitted for standard circuits in various installation methods and with different protective devices.
Then you can compare the circuit lengths with the resistance values given in appendix I to give you maximum values for resistance.

For instance a 2.5/1.5 ring final circuit on a 32A MCB with 30mA RCD protection has a maximum length of 106m. (this is limited by voltage drop)
Therefore on 106m your r1 and rn would be 0.00741*106 =0.785Ω
your r2 would be 0.0121*106=1.28Ω

Similarly for a 1.0/1.0 6A lighting circuit the max length is 59m and so R1+R2 would be 0.0362*59=2.14Ω.
Thank u very much this is exactly what i wanted to know.
 
Measure the ring final circuit readings i got a ze of o.14 at db on tns system i got a reading of 0.55 for r1 +r2 i would like to know what is the maximum reading allowed .
you mean R1 +R2. note capitals. add |R1+R2 +Ze. that will give you the Zs for the circuit. Zs must be < the max. value in (tables) for the In of the OPCD.
 
you mean R1 +R2. note capitals. add |R1+R2 +Ze. that will give you the Zs for the circuit. Zs must be < the max. value in (tables) for the In of the OPCD.
I have seen videos where they directly measure the zs through a megger meter. I that reliable or is it better to do the calculatio.
 

Reply to R1+r2 reading and r1,r2 and rn on ring final in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top