In design or initial verification of a circuit you do the calculation to ensure it is safe to power up. Once the circuit is powered then measurement of Zs is a standard, fairly reliable and common method of ensuring that your circuit is compliant with the disconnection times required. Measured Zs can be lower than calculated Zs and so the calculation is the worst case scenario used for safety.
 
If you have the On Site guide then in table 7.1 in chapter 7 this lists the maximum length of cable permitted for standard circuits in various installation methods and with different protective devices.
Then you can compare the circuit lengths with the resistance values given in appendix I to give you maximum values for resistance.

For instance a 2.5/1.5 ring final circuit on a 32A MCB with 30mA RCD protection has a maximum length of 106m. (this is limited by voltage drop)
Therefore on 106m your r1 and rn would be 0.00741*106 =0.785Ω
your r2 would be 0.0121*106=1.28Ω

Similarly for a 1.0/1.0 6A lighting circuit the max length is 59m and so R1+R2 would be 0.0362*59=2.14Ω.
Where do u get the value of 0.00741?
 
In design or initial verification of a circuit you do the calculation to ensure it is safe to power up. Once the circuit is powered then measurement of Zs is a standard, fairly reliable and common method of ensuring that your circuit is compliant with the disconnection times required. Measured Zs can be lower than calculated Zs and so the calculation is the worst case scenario used for safety.
Zs includes parallel earth paths eg structural metal of the building ,bonding etc. which rightly stated lowers the measured Zs value also if the circuit has a RCD/rcbo the test current used is lowered as not to trip the RCD/rcbo during the test therefore you get a higher Zs .
 

Reply to R1+r2 reading and r1,r2 and rn on ring final in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
486
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
956
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
920
I thought I'd add a few photo's of the overall situation we find ourselves in and the general standard of the building work, which is why going...
Replies
9
Views
394

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top