M
mr2pep
Hi,
Hoping someone can help.
I went to a job today where the householder had sixteen downlights installed less than twelve months ago, (no test sheet or certificate for the install), the complaint being that bulbs (240V GU10) are always blowing. I pulled the downlights and checked connections, all seem ok.
The downlights are split in to two circuits of eight and a central pendant. Controlled by two three gang, two way switches, one lot of eight is wired one way and the other eight and pendant are wired two way.
So I did a R1+R2 test on the eight downlight two way circuit, with the switches closed I got a reading of 1.2 ohms and switches open a reading of >1999 ohms. However without moving the meter or leads I flicked the switches on the two other circuits and redid the test and got readings of 53.4 ohms and 23.2 ohms, surely the other two switches should not interfere and I should still have got readings of >1999?
Am I correct in that reasoning? Or am I an idiot and missing something?
Regards, Paul.
Hoping someone can help.
I went to a job today where the householder had sixteen downlights installed less than twelve months ago, (no test sheet or certificate for the install), the complaint being that bulbs (240V GU10) are always blowing. I pulled the downlights and checked connections, all seem ok.
The downlights are split in to two circuits of eight and a central pendant. Controlled by two three gang, two way switches, one lot of eight is wired one way and the other eight and pendant are wired two way.
So I did a R1+R2 test on the eight downlight two way circuit, with the switches closed I got a reading of 1.2 ohms and switches open a reading of >1999 ohms. However without moving the meter or leads I flicked the switches on the two other circuits and redid the test and got readings of 53.4 ohms and 23.2 ohms, surely the other two switches should not interfere and I should still have got readings of >1999?
Am I correct in that reasoning? Or am I an idiot and missing something?
Regards, Paul.