D

davidjones89

if someone could just explain this please, when conducting R1 + R2 tests on a radial lighting circuit and say the highest reading you get is 0.82 ohms, where do you cross reference the readings ? ie what would be to high a reading :confused:
 
A measurement of R1 + R2 is mainly used to prove continuity of protective conductors. However the readings you get from this test can be used to calculate the Earth Fault Loop Impedance (Zs) by adding it to Ze.

Zs = Ze + (R1 + R2)

The maximum Zs values are found on pages 48 - 50 of BS 7671 (Tables 41.2, 41.3, 41.4 and 41.5). The values in these tables should be multiplied by 0.8 (rule of thumb) and the measured or calculated Zs should not exceed this corrected value.

A reading of 0.82Ω on a 6A lighting circuit is quite low. If it is wired in 1.5/1mm² then from the conductor resistance table on page 166 OSG the length of the circuit is only 27m [0.82 ÷ (30.2 ÷ 1000) = 27m]. The maximum length for a 6A (Type B) lighting circuit is 90m (limited by voltage drop) from Table 7.1 OSG giving you a maximum measured R1 + R2 of 2.71Ω [90 x (30.2 ÷ 1000) = 2.71Ω] and the maximum Zs is 6.13Ω so you're ok.

Hope that helps. ;)
 
Last edited by a moderator:
that depends on the length of the circuit , you can calculate the measurement by the resistance of the cable x length , but not easy to do in a house thats wired just esti mate but what you could do is take a Ze reading then a Zs reading and take one from the other and this should give you your R1 and R2 , but normally anything over 2 ohms should be looked at as a high reading ,thats a level i set for my self not in the regs , over the years you get used to what normal readings should be , and anything below that should be ok and if the readings of the Zs are ok its fine
 
I think we have had this raised before but if you have a Ze and a Zs then surely you can get R1+R2 by calculation In other words R1+R2 = Zs - Ze
 
I think we have had this raised before but if you have a Ze and a Zs then surely you can get R1+R2 by calculation In other words R1+R2 = Zs - Ze


You can do that quite simply.


The only slight concern is that measuring a Zs is il-advised on some circuits where it can contravene the electricity at work regs. (Working live) - This is the opinion of the NICEIC as far as I am aware.

I myself, measure Zs as you have suggested.
 
that depends on the length of the circuit , you can calculate the measurement by the resistance of the cable x length , but not easy to do in a house thats wired just esti mate but what you could do is take a Ze reading then a Zs reading and take one from the other and this should give you your R1 and R2 , but normally anything over 2 ohms should be looked at as a high reading ,thats a level i set for my self not in the regs , over the years you get used to what normal readings should be , and anything below that should be ok and if the readings of the Zs are ok its fine

The problem with doing it this way is that when you measure Zs you do so with bonding in place which give you parallel paths to earth and more than likely a lower reading than the sum of Ze + (R1+R2).

So as Ze is measured with bonding disconnected simply taking Ze from Zs will not give you a true R1+R2.
 
Last edited by a moderator:
Jud
I hear what you say about a true reading but would point out that this will always be the case with parallel paths as the procedure is quite specific you only disconnect the main earth to take the true Ze reading. I take it this was taken into account when the procedures were written up
 
I'm sorry, I'm not with you. Which procedures are we talking about.:confused:

A measurement of Zs with parallel paths will give you a lower reading than calculating it (Zs = Ze + (R1+R2)) and therefore cannot be relied upon to calculate R1+R2 by taking away Ze as this would in turn give you a lower R1+R2 than you would get by measuring it in the normal way.
 
Last edited by a moderator:
As JUD says, the measurment of true Ze will be different to the value of Ze measured in the Zs reading as parallel paths will have been re-introduced in order to carry out the Zs test.

Thats a mouthful.

This is why when you truly take the measurments you will find that 9 times out of 10, R1+R2 is never equal to Zs-Ze
 
I came up with 2 but it's been a long day. Parallel paths and if measuring Zs on a socket with a plug connector the contact may be more reliable than probe points. please give me the answer

Could it be something silly like test leads not nulled when doing R1+ R2 ?
 

Reply to R1 + R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top