My end to end readings for r2 are lower than the r1 end to end readings. (r1- 0.39 and r2 - 0.17) As it’s been wired in twin and earth my r2 should 1.67x bigger (r2 - 0.65). This is due to the parallel paths of steel conduit fixed on to metal caddy straps and metal stud frames. Usually you would disconnect the fly leads from the back boxes so you can get an accurate r2 reading. But due to flats being signed off and finished I’m restricted on doing that, so I’m wondering if the low r2 reading (0.17) is acceptable to write down. This will also give a much lower R1+R2 reading as a result.Just read the thread, left wondering what is the problem ?
No requirement to confirm on a ring.Is there any requirement for the cpc of a RFC to be a 'ring' at all? A RFC in metal conduit, with the conduit being used as the cpc. A RFC in plastic conduit, with a single cpc (of adequate cross section) serving things other than sockets in the conduit system, with spurs to the individual sockets.
Did you test any of the wiring at the first fix stage?
Often, but not always:Is there any requirement for the cpc of a RFC to be a 'ring' at all? A RFC in metal conduit, with the conduit being used as the cpc. A RFC in plastic conduit, with a single cpc (of adequate cross section) serving things other than sockets in the conduit system, with spurs to the individual sockets.