Simples mate. You link live to armour at the each point, and thats your reading. As armadillo sparks mentioned, the only other option is a wander lead, and measure R2.

But surely that would be measuring an R2 that your not using? Using a wander lead is also measuring an R2 that isn't being used I.E the SWA?
 
As it is a TT system the chances are that your going to have to protect that sub main distribution circuit with an RCD as you will most likely not get a low enough disconnection of 1 second if it over 32 amps or 0.2 for under with just a normal MCB/FUSE. So for the Zs of the circuit you would put 500ohms if your using a 100mA RCD, and then test for times.

I normally would calculate R1 + R2 for a SWA cable that is utilising the armour as a CPC as such. using a wander lead, measure the R1 and then the Armour R2 and then combine it with the Ze to find the Zs.[/QUOTE]

I agree, but again wouldn't you be calculating for an R2 that isn't being used?
 
As it is a TT system the chances are that your going to have to protect that sub main distribution circuit with an RCD as you will most likely not get a low enough disconnection of 1 second if it over 32 amps or 0.2 for under with just a normal MCB/FUSE. So for the Zs of the circuit you would put 500ohms if your using a 100mA RCD, and then test for times.

I normally would calculate R1 + R2 for a SWA cable that is utilising the armour as a CPC as such. using a wander lead, measure the R1 and then the Armour R2 and then combine it with the Ze to find the Zs.[/QUOTE]

I agree, but again wouldn't you be calculating for an R2 that isn't being used?

What R2 are you not using, if you have a 2 core cable and armour CPC. ?
 
Why is this? Which reg?

Thanks

411.5.1

Had to look that up :D

As an example I had to go to a farm where the labourer had driven a tractor through the yard with the forks up, he snapped a 16mm split con overhead that it turned out was earthed at the barn end. The fuse had not blown and when I arrived I found the split neatly coiled up by the house still live!
 
Last edited:
IMO the earth for the DB cicuit has to be taken back to the main board. The rod in the garage is is in addintion for final circuits in the garage. I would deffo run seperate earth.

let us know what you end up doing :)
 
I dont like the sound of this circuit. Why dont you in the house terminated the swa into a metal adaptable box using the earthings rings and then run a cpc from banjo back to the DB HOUSE CPC terminal. Then you have the circuit cpc connected as to normal practises.
If you cant get an R1/R2 the way it is now i would have thought that is a code 1 non compliance.
 
I suppose it's a matter of choice, Like Malcolm says his preference is maybe to use the Armour as cpc, some peoples is to run a single cpc, I prefer the seperate because it's how I was taught and it's what Ive always done
 
I dont like the sound of this circuit. Why dont you in the house terminated the swa into a metal adaptable box using the earthings rings and then run a cpc from banjo back to the DB HOUSE CPC terminal. Then you have the circuit cpc connected as to normal practises.

That's exactly what I have done.

Thanks all :flowers:
 

Reply to R1 + R2 test on SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
totally agree
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top