hi all just reading up on continuity testing (r1+r2 test) say i have a ring main of 40m long serving 10 sockets..

the reading i have got is say 0.35ohms

but on 1 socket i have a higher reading of 0.46ohms

now i have learnt at collage this may be caused due to a loose connection

could this also be due to a spur?

are spur readings usally higher
 
High R1&R2 readings can result from loose connections, however the r1, rn & r2 tests would normally be done prior, and in doing this, the loose connections will become apparent. The most common example for high R1&R2 readings used in syllabus is a spur, or 'ring within a ring' arrangement. I am surprised that loose connections was used as an example.
 
The R1R2 reading of a ring with a spur will be the R1R2 of the ring ,plus the R1R2 of the cable between the point of connection to the ring and the socket served by the spur.
 
please can u expand on ring within a ring?

a ring within a ring is pretty much what it says where a second ring has been added to the original, in itself this is not a problem unless the ring gets broken somewhere then you will have a ring with a radial attached when testing you would find all sockets on the ring read as they should but the radial readings will increase as you move outward
 
Can u give me some examples of what reading u would expect if you were to plug in ur tester to a spur please sorry about caps

Say the R1+R2 reading for the socket you're testing at is 0.35 Ohms and a spur has been taken from this point, say 10 metres of 2.5/1.5 pvc/pvc cable then your R1+R2 at the spur will be approximately 0.45 Ohms (allowing 0.10 Ohms for the spurred length of cable).

When this value (assuming it is the highest on the circuit) is added to the Ze or Zdb, you have the Zs for the final circuit.
 
High R1&R2 readings can result from loose connections, however the r1, rn & r2 tests would normally be done prior, and in doing this, the loose connections will become apparent. The most common example for high R1&R2 readings used in syllabus is a spur, or 'ring within a ring' arrangement. I am surprised that loose connections was used as an example.

It annoys me too, that a loose connection is generally used as an example for high readings, when it could be a multitude of sins causing it - However I believe that they use that example as it is the most common cause.
 
Say the R1+R2 reading for the socket you're testing at is 0.35 Ohms and a spur has been taken from this point, say 10 metres of 2.5/1.5 pvc/pvc cable then your R1+R2 at the spur will be approximately 0.45 Ohms (allowing 0.10 Ohms for the spurred length of cable).

When this value (assuming it is the highest on the circuit) is added to the Ze or Zdb, you have the Zs for the final circuit.
nice and clearly put, IQ.
 

Reply to r1+r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top