r1 r2 through conduit | on ElectriciansForums
Discuss r1 r2 through conduit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
N
nicsin02
Hi guys, as the title suggest how do u test the R1 R2 value or R2 continuity if the sockets are earthed via the metal conduit?
Thanks guys
nicsin, I take it you haven't got a problem with R1 & R2 on a circuit wired in T&E.
Conduit (or Trunking) is just a conductor like the bare core in T&E, nothing magical or mysterious about it!
Remember, you'll invariably get much lower R2 readings than T&E.
Much, much lower!! lol!!
Yeah but normally you would separate the c.p.c with twin and earth and measure between??
If your only cpc is the Conduit then you cant do a R1 + R2 due to parallel paths. Take your R1 inspect teh the conduit throughout and prove conitnuity.
If you have a seperate cpc within and you can isolate the cpc throughout from the Conduit then yes you can record a R1 + R2.
Take a Zs reading at the socket and thats about it.
Reply to r1 r2 through conduit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Agree when you have a Senior Moment how is that still allowed, especially with all the regulations in place now, always a dangerous situation in...
I believe that it is incorporated into the 5 days. But will double check. Thanks.