If your only cpc is the Conduit then you cant do a R1 + R2 due to parallel paths. Take your R1 inspect teh the conduit throughout and prove conitnuity.

If you have a seperate cpc within and you can isolate the cpc throughout from the Conduit then yes you can record a R1 + R2.

Take a Zs reading at the socket and thats about it.

At last!! lol!!

I was wondering when or even if someone was going to come up with the correct overview of testing a conduit installation. Though why anyone would install a separate CPC in a conduit installation still eludes me!! lol!!


Or you could hire a Ductor that delivers 25amp to test the conduit
smile.png



I wonder how many of the younger members here even know what your talking about, let alone ever seen or used one?? ...lol!!​



 
Was it also known as a "Clare" tester, have distant memories of sparking conduit joints in our apprentice training centre

Yes!!

Normally came in a wooden case, but have seen metal cased units too!! Last time i've seen one being used in the UK was 20 years ago, when i was witnessing the testing and commissioning of a large shopping centre. Pretty pointless testing continuity on this installation, as the whole building was metal framed throughout and all the landlords (for want of a better term) electrical installations, metal containment, etc was solidly fixed to this frame work. Not a single failure, or even remotely close to a failure was seen throughout the whole building!! lol!!
 
I use a Clare tester in the workshop for proving bonding on the cabinets that we manufacture; that gives a wee spark if the contact isn't good enough!

They can give you more than a Wee Spark just by making a slowish contact to a solidly earthed/bonded testing point!! lol!!

I've engraved my name on the inside of 20 X 20cm galvanised pull boxes with these testers in my youth!! lol!!
 

Reply to r1 r2 through conduit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
689
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
969

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top