If your only cpc is the Conduit then you cant do a R1 + R2 due to parallel paths. Take your R1 inspect teh the conduit throughout and prove conitnuity.
If you have a seperate cpc within and you can isolate the cpc throughout from the Conduit then yes you can record a R1 + R2.
Take a Zs reading at the socket and thats about it.
At last!! lol!!
I was wondering when or even if someone was going to come up with the correct overview of testing a conduit installation. Though why anyone would install a separate CPC in a conduit installation still eludes me!! lol!!
Or you could hire a Ductor that delivers 25amp to test the conduit
I wonder how many of the younger members here even know what your talking about, let alone ever seen or used one?? ...lol!!