Guys looking for some opinions here.
for talking sake we have a rfc r1=0.62 rn=0.62 and r2 =1.03
ok excellent we have correctly configured rfc.
onto (R1+R2) if going by the equation (r1+r2)/4 we end up with 0.41ohms
obviously as we are testing we will be aware of the higher reading at Spurs, but if you were getting higher than expected readings at socket outlets what +/- tolerance would you use before issuing a code and what code would you issue on an EICR?
I understand some would say why not investigate further and rectify but our client just wants a condition report returned as is, without any repairs carried out unless exposed live parts etc( I know it's daft but that's what they want )
TIA
for talking sake we have a rfc r1=0.62 rn=0.62 and r2 =1.03
ok excellent we have correctly configured rfc.
onto (R1+R2) if going by the equation (r1+r2)/4 we end up with 0.41ohms
obviously as we are testing we will be aware of the higher reading at Spurs, but if you were getting higher than expected readings at socket outlets what +/- tolerance would you use before issuing a code and what code would you issue on an EICR?
I understand some would say why not investigate further and rectify but our client just wants a condition report returned as is, without any repairs carried out unless exposed live parts etc( I know it's daft but that's what they want )
TIA