S

solavie

I was asked to add 3 extra sockets to a bedroom. It is a one ring supplying upstairs and downstairs with no RCD. Kitchen has a different ring.

When doing R1+R2 with cross joining Live & cpc at cu, I get a reading of 0.23 ohm upstairs and it keeps rising to 1.01 ohm downstairs.

Same problem with R1+Rn, I get 0.16 to 0.89 ohm

I measure r1 as .28, rn as 0.26 and r2 as 0.40

Insulation resistance is >299 on all .

Ze is 0.24 ohm on TNS

Planning to put an RCBO on the circuit.

Advise appreciated.
 
All upstairs is 0.23?

Downstairs could be a series of spur off spurs or a second ring tagged onto the upstairs ring
 
Last edited:
Have you definately identified each leg of the ring final and cross connected them correctly, if they are gradually rising from socket to socket as you go around the ring then it may be that you haven't, or it could be spurs as mentioned already?
 
Not that it would make that much of a difference, but it was once common practice, where a single ring circuit covered both up and downstairs, to wire the upstairs sockets as a ring and spur of the upstairs sockets to the downstairs sockets. Saved a hell of a lot of cable. ...lol!!! The clue being 3 X cables at the upstairs socket positions. Alternatively the downstairs sockets could have been spurred off the ring cable via JB's....
 
Yes, I have Definitely cross the wires as I could see the grey PVC cable coming into the CU. I will be going back there and will try the wires differently.

There is only one 2 wires going up from consumer unit. There is also a ring for kitchen and a ring for garage where the cu is situated. There is an extension on the ground floor (conservatory where I got the highest R1+R2.

The sockets are old and the wires has been crossed together before going into the sockets. Still that is quite a big difference. I have removed quite a few sockets and tighten the wires on some I had a few good turns.

i changing the wires round does not help, I guess it will be a job of disconnecting all the sockets to try to identify if there is any crossed circuit.

Cheers
 
If you had a perfect ring circuit and had crossed connected wronr, you probably wouldn't be getting the same reading for your upstairs sockets though
 
Upstairs reading goes from about 0.23 to 0.30 ohm. Downstairs getting 60 to 1.01 ohm.


Will double check everything tomorrow.
 

Reply to R1+R2 unusual reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top