R2 help please | Page 2 | on ElectriciansForums
Discuss R2 help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Sorry, we seem to be posting ahead of each other anticipating what the next 'reply' is going to be. I would try an insulation test on the 3 circuits with all cable disconnected to confirm whether or not there are N-E faults present. If there are N-E faults then your parallel path is via the N-E fault/s and the neutral bar. i.e. E to N fault in one circuit, linking at the neutral bar then N to E fault in the other circuit thus linking the two CPCs under test.
This is getting more strange by the minute, all the 3 circuit cables are disconnected at both the consumer unit and cooker unit, immerser switch and whatever the central heating connection outlet/socket, and you are still getting continuity between the disconnected CPCs is that right?
Yeah ok' I'll look in tomorrow but I'm thinking now that some cowboy wired the house 10 years ago and there may be something sinister going on like a huge non compliant joint hidden under the floor somewhere. Hope not though.
No that's not right. I did not disconnect all three cables but I will and so the IR tests of all three.
If they did, it was an approved contractor doing all the new builds! I will reserve judgement until I have done all the tests. I have already found IR value of 1.5 M ohms on the two RFC's. Its a new house just about!!
When carrying out continuity tests care should be taken to locate and disconnect where practicable any extraneous conductive paths connected in parallel to the installation.
If you're disconnecting the CPC's I'd recommend disconnecting the L & N's on each circuit in turn so you can be sure that you have the correct ones matched up.
Reply to R2 help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Very technical :D
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...