It is very confusing as on the test sheets it does say R1+R2 OR R2, implying just an R2 would be acceptable. I was scratching my head thinking how is that going to comply with the required times.
Just because R2 is all you need to record does not mean that is all you should test.
 
R2 is best used when doing EICR's to light fittings.

For new installation work the R1+R2 is best, then you can confirm polarity at the same time.

Would then changing a consumer unit count as new installation work as you are not installing any cables they are existing in regards to R1+R2. Think about what i'm actually asking here instead of getting boot in. (I know it would be an EIC before you start with the funny answers). If you dont get the question just ask me, cheers
 
As you are changing the consumer unit you have to prove by means of testing that existing circuits are safe to be energised.
 
As you are changing the consumer unit you have to prove by means of testing that existing circuits are safe to be energised.

Yeah i get that, but
you haven't altard as such any circuits from CU onwards so do you still need to R1+R2?
 
Would then changing a consumer unit count as new installation work as you are not installing any cables they are existing in regards to R1+R2. Think about what i'm actually asking here instead of getting boot in. (I know it would be an EIC before you start with the funny answers). If you dont get the question just ask me, cheers

Originally Posted by Murdoch
R2 is best used when doing EICR's to light fittings.

For new installation work the R1+R2 is best, then you can confirm polarity at the same time.


You need to listen and learn what the guy is trying to tell you mate..............he knows what he's talking about.
Out of interest..............how old are you?
and that is not asked in any way shape of form in a patronising fashion you ignorant young idiot..............last few words were a joke btw:)
 
Originally Posted by Murdoch
R2 is best used when doing EICR's to light fittings.

For new installation work the R1+R2 is best, then you can confirm polarity at the same time.


You need to listen and learn what the guy is trying to tell you mate..............he knows what he's talking about.
Out of interest..............how old are you?
and that is not asked in any way shape of form in a patronising fashion you ignorant young idiot..............last few words were a joke btw:)

around 40

- - - Updated - - -

Of course you do. I don't know what it is with trying to avoid doing an R1 + R2.

lol yeah i guess so
 
Of course you do. I don't know what it is with trying to avoid doing an R1 + R2.

O.K. im not trying to avoid you miss uder stand again, but im probably not explaining well either.
If you actually do a complete rewire its easy to do R1+R2, just bare cables hanging
Where as if you change a CU in an existing u still got hanging lights things plugged in, just seems so much more headache......
 
I do, its called cutting corners. A bit like not knowing where the circuits go, what they feed, or bothering to unplug appliances.

Crxp workmanship.

Hope your not referring to me, with your increasing positive input, how can i be cutting corners if im here on this site asking you the correct way to do it!
 
Last edited:

Reply to R2 option over R1+R2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
946
  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
594

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top