Hi All,
Rewired a kitchen today and part of the downstairs ring, the old twin & earth is 2.5 and 1mm earth and obviously the new wiring 2.5 1.5 twin.Problem being, as i carried out the ring continuity test
live and neutral 0.32
earth 1.24???
As part of the ring is 1mm iam aware that i should be expecting a reading of 0.80 i checked all sockets and the d/b for any loose connections almost all of the sockets are brand new appart from 2 which look about 2-3 years old.
My boss is adamant that the readings should be bang on or just out!!having checked all sockets and d/b im stuck any ideas???
thanks