Are these readings for r2 (not R2) too high?

kitchen ring: r1= 0.13 rn = 0.12 r2 = 0.33
cellar/living room ring : r1= 0.15 rn = 0.15 r2 = 0.40
Bedroom1 and 2: r1= 0.48 rn = 0.48 r2 = 1.17

what could be the problem if so?

Thank you for your skills

Si.
 
Hi sivoodoo

Are the cables in question new or old?

Could be that the cpc be 1.0 mm. This would fit as the figures in bold a 2.5 times greater than the other figures which would fit with a 2.5 / 1.0 cable.
 
Im not sure on the cpc size, whats the best way to tell?

Also where can i find a table that will give me the factors for different size conductors?
i.e 1.667 for 1.5mm etc.
Thanks
 
I don't know where the information can be found, but I think it can be calculated:

2.5 / 1.5 = 1.6666666667 (rounded up = 1.667)

2.5 / 1.0 = 2.5

Are the cables red and black ?
 
The figures suggest to me that the cpc is 1.0mm. I believe that in the past there were 2.5/1.0 cables.

Is it that the figures just don't make sense or are they outside the regulations?
 
I was presuming they were 1.5mm cpc, but the calculations point to 1mm cpc, Im happy with this, i need a tool to measure the diameter of conductors as i find it hard to tell on the smaller cables.

Thanks
 
Im not sure on the cpc size, whats the best way to tell?

Also where can i find a table that will give me the factors for different size conductors?
i.e 1.667 for 1.5mm etc.
Thanks
hi S,
maybe this will help-(you could use crimp lugs to determine size.)
I think this is from GN1
values resistance of copper at 20 oC mohm/m (move decimal point 3spaces to get ohm/metre)
1mm----18.10
1.5mm--12.10
2.5mm---7.41
4mm-----4.61
6mm-----3.08
10mm----1.83
16mm----1.15
 

Reply to r2 readings too high? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top