Hi there,
Been to quote a new DB change today...whilst inspecting the installation there are some things that need addressing.( TT System) The main problem was an Ra reading of 748 Ohms!!
Can this simply be sorted out by adding another electrode, or driving in a deeper one?
Thanks.
 
Hi there,
Been to quote a new DB change today...whilst inspecting the installation there are some things that need addressing.( TT System) The main problem was an Ra reading of 748 Ohms!!
Can this simply be sorted out by adding another electrode, or driving in a deeper one?
Thanks.


Where was the rod located, Sheltred? dry area? etc

Was it a proper 3 lead test?
 
Last edited:
[FONT=&amp]The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a Ra=200 Ohms will be more stable than a 1.5m rod with a Ra=100 Ohms.[/FONT] Although the regulations suggest Ra should be below 200 Ohms for stability it's good practice to aim for less than 100 Ohms to allow sufficient headroom for seasonal changes of environmental conditions. Use good quality 5/8" coupled rods in an inspection pit for mechanical/corrosion protection of the termination.
 
Last edited by a moderator:

Reply to Ra Reading? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
789
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top