FYI: This DIYer has a first class Electrical Engineering degree. However that was many years ago and I am far from up to speed with currect Regs. I had hoped that this forum would provide reliable advice, rather than facetious comments.

Forget the degree, just use a little common sense!
Every joint is a potential point of failure, common sense says you don't add a load of unnecessary joints.
If you are insistent on adding unnecessary joints then why not use 4mm for the branches?
 
If you are insistent on adding unnecessary joints then why not use 4mm for the branches?
1. I have already agreed that 4mm throughout would be better.
2. The "unnecessary" joints are due to my understanding that there is a max cable length.
 
What a load of utter nonsense, how can people get away with publishing such Ill informed and incorrect rubbish?

Ignore the ramblings of strangers on the internet and follow the wiring regulations!
I think it's on about the volt drop for clipped direct t&e it doesnt go into enough detail though
 
After 33m the volt drop on a 4mm² cable will exceed the 5% limit indicated by the wiring regulations.
A run of cable in smaller size than the supply cable would be considered a spur, rather than a branch.
It is recommended that the number of spurs is fewer than the number of sockets directly on the circuit.

Whilst this is a potentially possible solution it is by no means ideal, also you can have exactly the same arrangement in 4mm² cable as you have in 2.5mm² cable you will have the same cable length, which is presumably less than 33m.

If you were to run the spurs as you have suggested then you are even more likely to have problems with voltage drop as the reduced conductor size will increase the volt drop and so reduce the allowable circuit length.
 
FYI: This DIYer has a first class Electrical Engineering degree. However that was many years ago and I am far from up to speed with currect Regs. I had hoped that this forum would provide reliable advice, rather than facetious comments.

It is clear your not up to date with regulations and tbh Electrical Engineering does not in itself give you the knowledge for domestic work so with all respect I would ignore the invited comments and let's move on with the thread ...

We all know the OP's background now ... had he answered my post 2 we could have avoided all this, so can we either offer good advice or refrain from comment
 
Last edited:

Reply to Radial circuit and the use of spurs in the DIY Electrical Advice area at ElectriciansForums.net

Similar threads

An extra joint box isn’t a massive issue… use a wago box, with proper wagos. Nice and small will fit up through downlight hole. Wago box should...
Replies
2
Views
1K
Sorry, yes they should be ok.
2
Replies
25
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top