Hello all,

Just had an electrician wire in a radial circuit in my house to my loft as I use the space for my home theatre equipment & wanted a dedicated circuit for the equipment as its consists of quite a few power hungry amps & devices.

He has wired the radial in 4.0mm2 twin & earth cable connected to a 32 amp breaker, normally I gather this would not be an issue & is common place in installations.

The problem I can see is the total length of the cable from the consumer unit to the equipment in the loft is 35 meters & after doing a little research it seems that voltage drop is going to be an issue with a cable of this length.

After using a calculator online for voltage drop the conductor size required for a 6.0mm2 to be below the 5% maximum voltage drop stated in the regulations.

That calculation is for a cable that has been surface clipped which is correct for the length of the run in the loft which is 22 meters long.

The length of the run going along & up the side of the house to reach the loft is 13 meters long & is inside 25mm conduit along with a 2.5mm2 & 1.0mm2 cable for other circuits in the house.

So am I correct in saying that using a 32 amp breaker in this situation is not appropriate & a 20 amp breaker would be the correct choice?

Alternatively the cable needs to be changed to a 6.0mm2 cable to be able use a 32 amp breaker to protect the circuit?
 
A radial circuit run in 4mm T&E cable and protected by a 32amp MCB is a standards circuit arrangement.

What is the total load of your “power hungry” devices? I can’t imagine that they come anywhere near 32amp.
 
A radial circuit run in 4mm T&E cable and protected by a 32amp MCB is a standards circuit arrangement.

What is the total load of your “power hungry” devices? I can’t imagine that they come anywhere near 32amp.

I will be totally honest I do not know what the total load is, I looked up all the manufacturer specs for all my equipment & I got some crazy figure like 80 amps when I added them all together so I presume these published figures are theoretical maximums but are not much use in the real world?

What is the best way to work out what my total load is?

If the voltage drop is a non issue is there any issues with the current carrying capacity of the cable due to it being in conduit & also with other cables?
 
Volt drop will not reduce by putting in a 20A breaker.

Have you used a part p registered electrician?

If so you will get or have already got a certificate that confirms compliance with the regs.
 
Hi MM - You are correct that if a bigger cable was used then less voltage would be dropped for any given load in accord with Ohm’s Law, but it’s unlikely to be something that affects the use you propose. If you post up an equipment list I’m sure load estimates will be forthcoming.
 
If you post up an equipment list I’m sure load estimates will be forthcoming.
That will be interesting. I would be surprised if the total load on the circuit (and therefore assumed design current) was anywhere near high enough to exceed max volt drop requirements.

Also how sure are you on the length of circuit? A quick calc shows that even if the design current was 32A you could run approx. 30m in 4mm before exceeding volt drop.
 
I will be totally honest I do not know what the total load is, I looked up all the manufacturer specs for all my equipment & I got some crazy figure like 80 amps
I rather think you are misunderstanding of misreading the amount of MAINS current that the devices require.
A 200 watt audio amplifier at full whack won’t pull much more current than a 60watt light bulb.
Have a look at the rating information on the back of your devices.
 
I will be totally honest I do not know what the total load is, I looked up all the manufacturer specs for all my equipment & I got some crazy figure like 80 amps when I added them all together so I presume these published figures are theoretical maximums but are not much use in the real world?

What is the best way to work out what my total load is?

If the voltage drop is a non issue is there any issues with the current carrying capacity of the cable due to it being in conduit & also with other cables?
what yous running up there, a recording studio or a pirate radio station. ?


remember it well. on my old valve radio.long before FM.
 
Hi MM - You are correct that if a bigger cable was used then less voltage would be dropped for any given load in accord with Ohm’s Law, but it’s unlikely to be something that affects the use you propose. If you post up an equipment list I’m sure load estimates will be forthcoming.
what yous running up there, a recording studio or a pirate radio station. ?
remember it well. on my old valve radio.long before FM.
I rather think you are misunderstanding of misreading the amount of MAINS current that the devices require.
A 200 watt audio amplifier at full whack won’t pull much more current than a 60watt light bulb.
Have a look at the rating information on the back of your devices.
There is quite a few pieces up there as this is a full fledged home theatre so here goes.

1. Arcam AVR30 Processor / Amplifier

2. Emotiva XPA-7 Amplifier - x2

3. Behringer NX6000 Amplifier - x3

4. Behringer NX3000 Amplifier

5. Buttkicker BKA1000-N Amplifier

6. Epson EH-TW9300 Projector

7. Xbox One X

8. Virgin Media V6 Box

9. Phillips Hue

10. Netgear GS116UK Network Switch

11. Netgear R7800 Network Router

12. MiniDSP 2X4 HD - X2

13. HDFury Vertex

That will be interesting. I would be surprised if the total load on the circuit (and therefore assumed design current) was anywhere near high enough to exceed max volt drop requirements.

Also how sure are you on the length of circuit? A quick calc shows that even if the design current was 32A you could run approx. 30m in 4mm before exceeding volt drop.
The total length of the cable is 35 meters but as you say I would need to be using 32 amps to start running into issues with voltage drop so I now need to now workout what my total load is but as all of you say it is highly unlikely I am going to be anywhere near 32 amps.

OP- is it conduit or plastic mini trunking? Haven't looked at the tables so not sure if it makes a difference to derating factor
Is it black plastic conduit in 25mm, it looks like this stuff.

https://www.toolstation.com/25mm-heavy-duty-pvc-round-conduit/p66251

4mm T&E is undersized for a 32A protective device if it is contained in conduit.
Thank you for that information, it seems this is my issue rather than voltage drop at this point from all the information I have received here.

Many thanks to all of you for your time & help, it is greatly appreciated.
 
Hi MM - so coool stuff there :)

Power wise, I just looked at item 3, the Behringer NX6000 Amplifier of which you’ve got 3. I was stunned to see the spec says ea of these has 2 by 3kW amps. Yep 18kW. Aghhh. Then I looked at the power cable, it’s a plug. And it’s labelled 820W each. So probably closer to 2.4kW rather than 12kW + some efficiency factor. But it does seem like you’re going to need some air handling plant up there.

[ElectriciansForums.net] Radial Circuit Cable Length
 

Reply to Radial Circuit Cable Length in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Replies
24
Views
1K
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top