Because a twin socket constitutes a spur as does a single see appendix 15 BS 7671
I get that bit Pete, what I meant by that was why the distinction between 2 sockets as singles, or 2 sockets as a double? I think Mark Ribbands comment probably hit the nail on the head
 
Odd set up, but surely no worse than a double socket spurred from the MCB of a ring final? Incidentally does anyone know why the regs say an unfused spur on a ring final can feed 1 double socket, but not 2 singles?

Years ago the regulations did allow two single sockets on a spur, but that was changed to being one point regardless of whether its a twin or single. I have no idea why the change was made, but would hazard a guess that it related to the increase in available appliances and use of electricity or else maybe it was found that this was leading to overloading.
 
It seems strange to me that a double socket is only rated to 20A (not commonly known) when you theoretically could have 26A plugged into them. Clearly it works this way, otherwise there would be fires left right and centre, but it does feel like there is an element of chance involved.
 
It seems strange to me that a double socket is only rated to 20A (not commonly known) when you theoretically could have 26A plugged into them. Clearly it works this way, otherwise there would be fires left right and centre, but it does feel like there is an element of chance involved.

The British standard requires that a twin socket be tested with a load of 20A made of of a 13A load and a 7A load. Manufacturers are free to make the total current rating whatever they like above this.
 
I would install a new 32 amp supply..
6mm t+e, cooker switch with socket.
3.6kw oven wired into switch
Hotplate plugged into socket
Or if the existing cable is ok then utilise that socket and then use 4mm instead of 6mm.
You shouldn’t have a 3.6kw load wired into a plug
 

Reply to Radial circuit help in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
438
  • Question
Why aren't you asking them?
Replies
5
Views
862

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top